From a control point of view a lot depends if you bought the model with an internal feedback position pot so your control system will know what position the actuator is at any specific time. If you lack that feedback option there is little point in driving the actuator at a variable speed in my opinion as you would have no idea where the actuator is in it's travel range and you would just be relying on the built in limit switches on the actuator to stop when travel reaches either end position. If you lack the feedback pot you are probably better off just driving the actuator with a DPDT relay that just applies voltage to the actuator at either polarity to travel the direction you wish and the actuator will stop via it's limit switches when it reaches an end point.
So the question that you need to ask is does your application require closed loop control or is simple open loop control good enough?
Lefty