max 31865 and pt100 showing wrong temp

Hi.

Im using an Leonardo with max 31865 + pt100 and get a value(temp) that is in room temp about +70 degrees to high.

Tried with 2 different types of library but whit same result. Tested with a different sensor and a different max31865 but with same result.

What have i done wrong?

Jonas

/**************************************************************************
 * MAX31865 Basic Example
 *
 * Copyright (C) 2015 Ole Wolf <wolf@blazingangles.com>
 *
 *
 * Example code that reads the temperature from an MAX31865 and outputs
 * it on the serial line.
 * 
 * Wire the circuit as follows, assuming that level converters have been
 * added for the 3.3V signals:
 *
 *    Arduino Uno   -->  MAX31865
 *    ---------------------------
 *    CS: pin 10    -->  CS
 *    MOSI: pin 11  -->  SDI (must not be changed for hardware SPI)
 *    MISO: pin 12  -->  SDO (must not be changed for hardware SPI)
 *    SCK: pin 13   -->  SCLK (must not be changed for hardware SPI)
 *
 *
 * This program is free software: you can redistribute it and/or modify
 * it under the terms of the GNU General Public License as published by
 * the Free Software Foundation, either version 3 of the License, or
 * (at your option) any later version.
 *
 * This program is distributed in the hope that it will be useful,
 * but WITHOUT ANY WARRANTY; without even the implied warranty of
 * MERCHANTABILITY or FITNESS FOR A PARTICULAR PURPOSE.  See the
 * GNU General Public License for more details.
 *
 * You should have received a copy of the GNU General Public License
 * along with this program.  If not, see <http://www.gnu.org/licenses/>.
 **************************************************************************/

#include <SPI.h>
#include <MAX31865.h>


#define RTD_CS_PIN   10


MAX31865_RTD rtd( MAX31865_RTD::RTD_PT100, RTD_CS_PIN );


void setup()
{
  Serial.begin( 115200 );

  /* Initialize SPI communication. */
  SPI.begin( );
  SPI.setClockDivider( SPI_CLOCK_DIV16 );
  SPI.setDataMode( SPI_MODE3 );

  /* Allow the MAX31865 to warm up. */
  delay( 100 );

  /* Configure:

       V_BIAS enabled
       Auto-conversion
       1-shot disabled
       3-wire enabled
       Fault detection:  automatic delay
       Fault status:  auto-clear
       50 Hz filter
       Low threshold:  0x0000
       High threshold:  0x7fff
  */
  rtd.configure( true, true, false, true, MAX31865_FAULT_DETECTION_NONE,
                 true, true, 0x0000, 0x7fff );
}



void loop() 
{
  rtd.read_all( );

  if( rtd.status( ) == 0 )
  {
    double temperature = rtd.temperature( );
    Serial.print( " T = ");
    Serial.print( temperature, 1 );
    Serial.println(" deg C" );
  }
  else 
  {
    Serial.print( "RTD fault register: " );
    Serial.print( rtd.status( ) );
    Serial.print( ": " );
    if( rtd.status( ) & MAX31865_FAULT_HIGH_THRESHOLD )
    {
      Serial.println( "RTD high threshold exceeded" );
    }
    else if( rtd.status( ) & MAX31865_FAULT_LOW_THRESHOLD )
    {
      Serial.println( "RTD low threshold exceeded" );
    }
    else if( rtd.status( ) & MAX31865_FAULT_REFIN )
    {
      Serial.println( "REFIN- > 0.85 x V_BIAS" );
    }
    else if( rtd.status( ) & MAX31865_FAULT_REFIN_FORCE )
    {
      Serial.println( "REFIN- < 0.85 x V_BIAS, FORCE- open" );
    }
    else if( rtd.status( ) & MAX31865_FAULT_RTDIN_FORCE )
    {
      Serial.println( "RTDIN- < 0.85 x V_BIAS, FORCE- open" );
    }
    else if( rtd.status( ) & MAX31865_FAULT_VOLTAGE )
    {
      Serial.println( "Overvoltage/undervoltage fault");
    }
    else
    {
      Serial.println( "Unknown fault; check connection" );
    }
  }

  delay( 3000 );
}

You are using a 4 wire (Kelvin connection)? Can you post a wiring diagram?
HowToPostCode & Attachments

Im using a 2-wire k-type.

Wiread it like this:

Max 31865 - Leonardo

CS - pin 10
SDI - pin 14
SD0 - pin 16
SCK - pin 15

"K type"? Is that a thermocouple or RTD? Can you post a link?

https://m.ebay.com/itm/3-3ft-K-Type-Screw-Thermocouple-Temperature-Controller-0-800-Sensor-Probe-X5-10/142345129346?hash=item21246e4d82:m:mUZaL6_ygisKiz1YnVTxW_A

This one. And its not an pt100.

And I thing i noticed the problem, need a diffrent module?

you can using MAX31865 with RTD not Thermocouple sensor. you can read this https://www.versasense.com/files/datasheets/MAX31865.pdf