Topic: Calculations for snubber circuit (Read 1 time) previous topic - next topic

Marciokoko

#15
Jan 09, 2018, 02:58 am Last Edit: Jan 09, 2018, 02:58 am by Marciokoko
Thanks Tony,

Could you explain how they got 780pF from this:




link
https://www.quora.com/How-do-I-pick-the-R-and-C-values-of-a-RC-snubber-what-are-the-most-important-equations

unLike

Have you given any thought about the in rush of the ac circuit running the compressor? The 10 amp contacts may roast or weld together when the 3/4HP motor starts. In the instant that the contacts close the motor current can reach 6 times the running current, until the motor windings are saturated. Find a relay that the contacts are rated for 20 amps, is my suggestion.
Some knowledge can be dangerous

Marciokoko

yikes!  Ok I took an AC clamp meter to my lines on the compressor:

white = 29 max
green = 28 max
black = gnd

So yes, 10A is too little.

But that doesnt mean its 57A draw is it?

Marciokoko

#18
Jan 12, 2018, 11:00 pm Last Edit: Jan 12, 2018, 11:03 pm by Marciokoko
I just noticed my relays ARE 30A!