Hi All,
Can I use 12 A relay shield for home appliances which operates on 230 volt ac ?
Hi All,
Can I use 12 A relay shield for home appliances which operates on 230 volt ac ?
It depends on the relay contacts rating and the appliance you are wanting to switch, and of course this depends on what relay shield you are using.
The relay contact ratings are their maximum. For example, a 230V, 12A relay can be used to switch 1 Amp at 120V.
If know the wattage rating of your appliance but not the current, power (Watts) is calculated as Voltage x Current. ...A 230V 1200W hair drier is drawing 5.2 Amps.
The relay's coil ratings are "exact" ...A relay coil that takes 12V @ 100mA, needs a 12V power supply/soruce that can supply the required 100mA.
No shield as such can be used safely for mains - there is not enough physical separation between
mains and low voltage stuff possible on a shield.
A separate relay board with adequate spacing and/or PCB cutouts to protect low voltage from
the mains side would be the right technology. It ought to be conformally coated too really...
I have a relay shield, with 250A, 5A rated relays.
Here's a youtube video of it controlling LED light strings.
and close up is attached.
At some point, a contactor might be a better choice.
He's not stated if he needs it to handle an inductive load.
Dwight
No shield as such can be used safely for mains - there is not enough physical separation between
mains and low voltage stuff possible on a shield.
I agree with that.
These days there are low-cost relay boards like THIS:that have built-in Optical Isolation. The board linked here has a relay rating of 10A at 230V.
There is also a 30A rated relay with optical isolation HERE:
There is some relay How-To on the ArduinoInfo.Info WIKI HERE: See the page HERE:
If you need to switch inductive loads or have EMI (ElectroMagnetic Interference) problems see the page HERE:
DISCLAIMER: Mentioned stuff from my own shop... but you can find these relays on Ebay etc...
I need to on off below mentioned devices
And i have below show Relay with Toshiba ULN2803APG
One other thing worth mentioning.
While a shield may well be suitable for domestic control of mains.
If it does not have UL and CE ratings your insurance may be invalid.
Also connecting it to your domestic supply will likely need a certified electrician to meet local electrical codes.
Thanks I will check with local electician
You have data on the top of relays. Important value for you is 7A 250V ~. All your devices are under max. switched current (7A). In case of higher current need you can add auxiliary relay (let say for 16A) with ~250V coil driven by shield relay.