@noiasca
The Serial print() are for debugging right now and will be removed but I do hear ya.
The void preTransmission(){} function stuff is part of the ModbusMaster Library. Those pins are for activating an RS485 Chip
The enums is a great idea.
@mugambi
Hey im not sure how i would use a struct for a state machine.
a pseudocode would be very desirable.
I was told to use a Switch case to make a State machine.
Is there another way? How would I use a Struct?
anyways, heres the code.
//Revision of JBOX with moxa and stride ioexpanders
#include <Wire.h> //For I2C comm
#include <Adafruit_GFX.h>
#include <LedHelper.h>
#include "Adafruit_LEDBackpack.h"
#include "Adafruit_LiquidCrystal.h"
#include<SPI.h>//serial peripheral interface
#include<Ethernet3.h>//for ethernet
#include<ArduinoRS485.h> //ArduinoModbus depends on the ArduinoRS485 lib
#include<ArduinoModbus.h>//for modbus tcp/ip
#include<ModbusMaster.h>//for oci417.10 rs485 interface with BMM
#include<pid.h>
#include "DEFINES.h"
#include "GLOBALS.h"
// OCI417.10 rs485 interface with BMM
ModbusMaster NODE;
//modbus tcp/ip communication declarations
byte mac[] = { 0xdE, 0xAD, 0xBE, 0xEF, 0xED};
IPAddress ip(128, 1, 1, 110); //needs to be similar to Acromag because will not connect
EthernetClient ethClient1;
EthernetClient ethClient2;
EthernetClient ethClient3;
EthernetClient ethClient4;
EthernetClient ethClient5;
EthernetClient ethClient6;
EthernetClient ethClient7;
EthernetClient ethClient8;
ModbusTCPClient modbusTCPClient1(ethClient1);
ModbusTCPClient modbusTCPClient2(ethClient2);
ModbusTCPClient modbusTCPClient3(ethClient3);
ModbusTCPClient modbusTCPClient4(ethClient4);
ModbusTCPClient modbusTCPClient5(ethClient5);
ModbusTCPClient modbusTCPClient6(ethClient6);
ModbusTCPClient modbusTCPClient7(ethClient7);
ModbusTCPClient modbusTCPClient8(ethClient8);
IPAddress serverIOEX1(128, 1, 1, 101); // IP of ioex1 STRIDE SIO-MB04DAS 4CH Analog Output
IPAddress serverIOEX2(128, 1, 1, 102); // IP of ioex2 STRIDE SIO-MB04DAS 4CH Analog Output
IPAddress serverIOEX3(128, 1, 1, 103); // IP of ioex3 STRIDE SIO-MB04DAS 8CH TC/mV Input
IPAddress serverIOEX4(128, 1, 1, 104); // IP of ioex4 STRIDE SIO-MB04DAS 8CH TC/mV Input
IPAddress serverIOEX5(128, 1, 1, 105); // IP of ioex5 STRIDE SIO-MB04DAS 8CH TC/mV Input
IPAddress serverIOEX6(128, 1, 1, 106); // IP of ioex6 MOXA IOLOGIK E1240 8CH Analog Input
IPAddress serverIOEX7(128, 1, 1, 107); // IP of ioex7 MOXA IOLOGIK E1211 16CH Digital Output
IPAddress serverIOEX8(128, 1, 1, 108); // IP of ioex8 MOXA IOLOGIK E1210 16CH Digital Input
//PID controllers
PID SUPER_HEAT_TT303 = PID(0.1, RO_PUMP_TOP_SPEED, RO_PUMP_AT_10_GRAMS_PER_SEC, 1000, 0, 0); //dt,max,min,kp,kd,ki
PID SUPER_HEAT_TT306 = PID(0.1, RO_PUMP_TOP_SPEED, RO_PUMP_AT_10_GRAMS_PER_SEC, 0.9, 0.01, 0); //dt,max,min,kp,kd,ki
PID STEAM_GEN_PID = PID(0.5, BLOWER_TOP_SPEED, BLOWER_RAMP_END , 5000, 0, 0);//dt,max,min,kp,kd,ki;//0.1,100,-100,0.8,0.01,0.5
PID BURNER_TEMP_CROSSOVER_PID = PID(0.9, 10000, 6500, 1000, 0, 0); //dt,max,min,kp,kd,ki;//
PID OPEN_SR_FUEL_PID = PID(0.9, 10000, 0, 100, 0.01, 0);//dt,max,min,kp,kd,ki;//
//Daughter Board periferals
SmallMatrix smallMatrix[3] = {SmallMatrix(0x70), SmallMatrix(0x71), SmallMatrix(0x72) };
LargeMatrix bigMatrix[3] = {LargeMatrix(0x73), LargeMatrix(0x74), LargeMatrix(0x75) };
Adafruit_LiquidCrystal lcd(0);
//telemetry
union floatToBytes {
char asBytes[4] = {0};
float asFloat;
pinMode(MAX485_RE_NEG, OUTPUT);
pinMode(MAX485_DE, OUTPUT);
// Init in receive mode rs485
digitalWrite(MAX485_RE_NEG, 0);
digitalWrite(MAX485_DE, 0);
Serial.begin(9600); // for dedbugging
Serial1.begin(9600);//FOR OCI MODULE rs485
NODE.begin(1, Serial1); //unit id1 on serial1
NODE.preTransmission(preTransmission);
NODE.postTransmission(postTransmission);
delay(500);//wait for system to boot up
pinMode(LED_PWR, OUTPUT);
digitalWrite(LED_PWR, HIGH);
pinMode(TRACO_24VDC, OUTPUT);
digitalWrite(TRACO_24VDC, HIGH);
pinMode(ESTOP_BREAK, OUTPUT);
digitalWrite(ESTOP_BREAK, HIGH);
//reseting wifichip
pinMode(7, OUTPUT);
digitalWrite(7, HIGH);
delay(50);
//start the Ethernet connection and the server:
Ethernet.begin(mac, ip);
integrityCheck();
connect_IO_Expanders();
readBtn();
readOCI();
CURRENT_MILLIS = millis(); //So as to not divide by zero on first looptime.
LOOP_MILLIS = millis();
lcd.begin(16, 2);
DB_INIT();
SENSOR_INTEGRITY_CHECK = true;
Serial.print("Error:"); Serial.println(ERROR); //debugging
Serial.print("GRN_BTN_FLAG: "); Serial.println(GRN_BTN_FLAG);
Serial.print("AMB_BTN_FLAG: "); Serial.println(AMB_BTN_FLAG);
Serial.print("ESTOP_FLAG: "); Serial.println(ESTOP_FLAG);
Serial.println(FSM_STATE);
LOOP_TIME = LOOP_MILLIS - CURRENT_MILLIS;
DB_RX();
error_Checker();
integrityCheck();
superheatTest();
readTCs();
readBtn();
readOCI();
readPTs();
blinkGRN();
blinkAMB();
readOut();
if (GRN_BTN_FLAG && !ESTOP_FLAG) {
switch (FSM_STATE) {
case INITIALIZE: //initialize
if (!SENSOR_INTEGRITY_CHECK) {
modbusTCPClient3.coilWrite(2, 1); //CH2 digital output xv909//ON
if (!COMBUSTION_PRESSURE_SWITCH) {
modbusTCPClient1.holdingRegisterWrite(40, BLOWER_PURGE_SPEED); //write channel 0 (BLWRSpeed)
modbusTCPClient7.coilWrite(9, 1); //BLWR_EN..The logic is opposite
if (DUN_PSL) {
Serial.print("Break due to DUN_PSL Switch: ");
Serial.println(DUN_PSL);
//check for RO water???//need another sensor
modbusTCPClient1.holdingRegisterWrite(40, OFF); //write channel 0 (BLWRSpeed)
modbusTCPClient7.coilWrite(9, 0); //BLWR_EN..
if (BMM_PROOF_OF_FLAME) { //get that flame out before proceed
if (!modbusTCPClient1.connected()) {
modbusTCPClient1.begin(serverIOEX1, 502);
if (!modbusTCPClient2.connected()) {
modbusTCPClient2.begin(serverIOEX2, 502);
modbusTCPClient1.holdingRegisterWrite(42, OFF); //write channel 2 ioex1 (FCV134)
modbusTCPClient2.holdingRegisterWrite(40, OFF); //write channel 0 ioex2 (FCV141)
if (!modbusTCPClient7.connected()) {
modbusTCPClient7.begin(serverIOEX7, 502);
modbusTCPClient7.coilWrite(6, OFF); //TWV308
modbusTCPClient7.coilWrite(4, OFF); //XV1100
modbusTCPClient7.coilWrite(3, OFF); //XV501
modbusTCPClient7.coilWrite(8, OFF); //BMM_CR2
modbusTCPClient7.coilWrite(7, OFF); //TWV901
modbusTCPClient7.coilWrite(2, ON); //CH4 digital output xv909
FSM_STATE = DEPRESSURIZE;
case DEPRESSURIZE: //depressurise reformer
if (PT420_STEAM_EJECTOR_PRESSURE >= ATMOSPHERIC_PRESSURE) {
PT420_STEAM_EJECTOR_PRESSURE = (modbusTCPClient6.holdingRegisterRead(5) * (.0125)) - 47; //ref:43016 read Channel 6 PT420
// PT420_STEAM_EJECTOR_PRESSURE = modbusTCPClient2.holdingRegisterRead(3022);
modbusTCPClient7.coilWrite(2, ON); //CH2 digital output xv909
modbusTCPClient7.coilWrite(2, OFF); //CH2 digital output xv909
//250 psi
if (PT213_RO_PRESSURE < 250) {
//just guessing on the fcv205 flow, as long as we stay beneath 250psi
modbusTCPClient1.holdingRegisterWrite(42, FCV205_AT_35_PERCENT); //write channel 2 (FCV205)//made steam at 1000//last 3000//~about 35 percent
modbusTCPClient1.holdingRegisterWrite(41, RO_PUMP_AT_10_GRAMS_PER_SEC); //write channel 1 (WP_Speed) made steam at 1*2000//last 3*2000
modbusTCPClient7.coilWrite(10, ON); //WP_EN..
modbusTCPClient7.coilWrite(9, ON); //BLWR_EN..
FSM_STATE = SUPERHEAT_TEST;
PREVIOUS_MILLIS = millis();
case SUPERHEAT_TEST://Superheat Test
//make sure we are closed//xv909
modbusTCPClient7.coilWrite(2, OFF); //CH4 digital output xv909
//monitor tc 407 & 408
//need a timer
if (CURRENT_MILLIS - PREVIOUS_MILLIS <= SUPERHEAT_TIMER) {
TT303_HX504_STEAM_OUT = modbusTCPClient3.holdingRegisterRead(42) * (0.095);
//guessing on 300 degrees centigrade
if (TT303_HX504_STEAM_OUT > 300) {
ERROR = 7; FSM_STATE = INITIALIZE; break;
FSM_STATE = BMM_OFF;
case BMM_OFF://bmm off //30 seconds;
if (CURRENT_MILLIS - PREVIOUS_MILLIS <= BMM_OFF_TIMER) {
modbusTCPClient7.coilWrite(8, OFF); //BMM_CR2 bmm off
FSM_STATE = BMM_ON;
case BMM_ON:
//bmm on //5 seconds
modbusTCPClient7.coilWrite(8, ON); //BMM_CR2 turn on
if (CURRENT_MILLIS - PREVIOUS_MILLIS <= BMM_START_TIMER) {
FSM_STATE = BMM_PURGE;
case BMM_PURGE:
//bmm purge
if (CURRENT_MILLIS - PREVIOUS_MILLIS <= BMM_PURGE_TIMER) {
FSM_STATE = BMM_IGNITION;
case BMM_IGNITION:
//BMM ignition
modbusTCPClient1.holdingRegisterWrite(40, BLOWER_IGNITION_SPEED); //write channel 0 (BLWRSpeed)
modbusTCPClient1.holdingRegisterWrite(42, FCV134_BURNER_FUEL_FLOW_IGNITION); //write channel 2 (FCV134)
if (CURRENT_MILLIS - PREVIOUS_MILLIS >= BMM_IGNITION_TIMER) {
if (!BMM_PROOF_OF_FLAME) {
ERROR = 8;
else {
FSM_STATE = BURNER_RAMP;
PREVIOUS_MILLIS_2 = millis();
case BURNER_RAMP:
//start burner ramp//15 minutes//900 seconds
//burner ramp is 4mins
//timing to reach 800c is 15 mins
TT511_SILICON_CARBIDE_OUT = (modbusTCPClient4.holdingRegisterRead(43)) * (0.095);
TT513_HX504_IN = (modbusTCPClient4.holdingRegisterRead(45)) * (0.095);
Serial.print("TT511: "); Serial.println(TT511_SILICON_CARBIDE_OUT);
Serial.print("TT513: "); Serial.println(TT513_HX504_IN);
Serial.print("Burner Ramp Timer 15 mins: "); Serial.println(CURRENT_MILLIS - PREVIOUS_MILLIS);
if (CURRENT_MILLIS - PREVIOUS_MILLIS >= BURNER_REACH_END_TIMER) {
if (TT511_SILICON_CARBIDE_OUT >= BURNER_TEMP_RAMP_END) {
FSM_STATE = STEAM_GEN;
if ( TT513_HX504_IN >= BURNER_TEMP_RAMP_END) {
ERROR = 11; FSM_STATE = INITIALIZE; break;
BLOWER_SPEED_FEEDBACK = modbusTCPClient6.inputRegisterRead(0);//10volts/10000counts
FCV134_BURNER_FUEL_FLOW_FB = modbusTCPClient6.inputRegisterRead(7);//ref:43028 read Channel 7 FCV134//~10079
Serial.print("Blower FB: "); Serial.println(BLOWER_SPEED_FEEDBACK);
Serial.print("FCV134 FB: "); Serial.println(FCV134_BURNER_FUEL_FLOW_FB);
if (CURRENT_MILLIS - PREVIOUS_MILLIS <= BURNER_RAMP_TIMER) {
if (CURRENT_MILLIS - PREVIOUS_MILLIS_2 >= 5000) {
//if(BLOWER_SPEED_FEEDBACK<=14030){
//modbusTCPClient1.holdingRegisterWrite(0x12,BLOWER_SPEED_FEEDBACK+220);}//write channel 0 blwr speed//44counts/sec
//if(FCV134_BURNER_FUEL_FLOW_FB<=16121){
//modbusTCPClient1.holdingRegisterWrite(0x14,FCV134_BURNER_FUEL_FLOW_FB+125);}//25counts/sec
modbusTCPClient1.holdingRegisterWrite(42, FCV134_BURNER_FUEL_FLOW_RAMP_END); //16121 best thus far, fuel
modbusTCPClient1.holdingRegisterWrite(40, BLOWER_RAMP_END); //7100 best thus far, blwr
else {
//modbusTCPClient1.holdingRegisterWrite(0x14,16121);//25counts/sec
//modbusTCPClient1.holdingRegisterWrite(0x12,13000);//write channel 0 blwr speed//44counts/sec
case STEAM_GEN://Steam generation
//steam gen timeout 30 mins
if (CURRENT_MILLIS - PREVIOUS_MILLIS >= STEAM_GENERATION_TIMER) {
ERROR = 9;
//PID control blower to acheive 170PSI pt304
BLOWER_SPEED_FEEDBACK = modbusTCPClient6.inputRegisterRead(0); //10volts/20000counts
steamGenPID();
if (PT304_TWV308_INPUT_PRESSURE <= 172 && PT304_TWV308_INPUT_PRESSURE >= 168) {
if (PSI_INIT_TIMER == false) {
PREVIOUS_MILLIS_1 = millis();
PSI_INIT_TIMER = true;
if (CURRENT_MILLIS - PREVIOUS_MILLIS_1 >= STEAM_AT_170PSI_TIMER && PSI_INIT_TIMER == true) {
BLOWER_SPEED_AT_170PSI = BLOWER_SPEED_FEEDBACK;
modbusTCPClient1.holdingRegisterWrite(40, BLOWER_SPEED_AT_170PSI);
modbusTCPClient7.coilWrite(3, ON); //XV501 ON
FSM_STATE = OPEN_SR_FUEL; PREVIOUS_MILLIS = millis(); PSI_INIT_TIMER = false; BURNER_TEMP_CROSSOVER = TT513_HX504_IN; break;
else {
PSI_INIT_TIMER = false; //If not in bounds of 170-psi, reset timer. Turn on xv501
modbusTCPClient6.coilWrite(3, OFF);
case OPEN_SR_FUEL:
//OPEN SR FUEL
//Point twv308 to reformer
modbusTCPClient7.coilWrite(6, ON); //TWV308//TWV308 ON//direct steam to reformer
modbusTCPClient7.coilWrite(5, ON); //XV801 On to induce gas feed to reformer
//assign percentage to fcv141 sr fuel flow control //fcv205 kicked to 50%
modbusTCPClient2.holdingRegisterWrite(40, FCV141_SR_FUEL_START_PERCENT); //write channel 4 (FCV141)
modbusTCPClient1.holdingRegisterWrite(43, FCV205_AT_50_PERCENT); //write channel 3 (FCV205)
//read fcv134 for burner temp control
if (!modbusTCPClient6.connected()) {
modbusTCPClient6.begin(serverIOEX6, 502);
FCV134_BURNER_FUEL_FLOW_FB = modbusTCPClient6.holdingRegisterRead(7);//read Channel 7 FCV134
if (CURRENT_MILLIS - PREVIOUS_MILLIS <= OPEN_SR_FUEL_TIMER) {
//pid burner control for 880C
BURNER_FUEL_CUT_OFFSET = BURNER_TEMP_CROSSOVER_PID.calc_reverse(BURNER_TEMP_CROSSOVER , TT513_HX504_IN);
Serial.print("BURNER_FUEL_CUT_OFFSET: "); Serial.println(BURNER_FUEL_CUT_OFFSET);
Serial.print("TT513_HX504_IN: "); Serial.println(TT513_HX504_IN);
modbusTCPClient1.holdingRegisterWrite(42, BURNER_FUEL_CUT_OFFSET);//write channel 2 (FCV134)
//pid srfuel control for 0.3g/second
FT132_NG_FEED_FLOW = modbusTCPClient6.inputRegisterRead(2);
FT132_ADJUSTED_MEASURE = (FT132_NG_FEED_FLOW * FT132_PIPE_DIA_CONV * FT132_COUNTS_TO_G_PER_SEC) - FT132_4MA_OFFSET;
SR_FUEL_OFFSET = OPEN_SR_FUEL_PID.calculate(SR_FUEL_CUT, FT132_ADJUSTED_MEASURE); //calc offset for FCV141
Serial.print("SR_FUEL_OFFSET: "); Serial.println(SR_FUEL_OFFSET);
Serial.print("FT132_ADJUSTED_MEASURE: "); Serial.println(FT132_ADJUSTED_MEASURE);
modbusTCPClient2.holdingRegisterWrite(40, SR_FUEL_OFFSET); //write channel 4 (FCV141)
//check conformance and restart time if out of bounds
if ((FT132_ADJUSTED_MEASURE > (SR_FUEL_CUT + 0.2)) || (BURNER_TEMP_CROSSOVER < (SR_FUEL_CUT - 0.2))) {
//reset timing if temp falls out of threshold
if ((BURNER_TEMP_CROSSOVER > (TT513_HX504_IN + 5)) || (BURNER_TEMP_CROSSOVER < (TT513_HX504_IN - 5))) {
else {
if (ERROR == 0) {
FSM_STATE = IDLE_MODE;
FSM_STATE = OPEN_SR_FUEL; PREVIOUS_MILLIS = millis(); break;
case IDLE_MODE:
//idle hold mode blower/burner pid
//3 mins idle ????
if (CURRENT_MILLIS - PREVIOUS_MILLIS <= 180000) {
//burner fuel PID
BURNER_FUEL_CUT_OFFSET = OPEN_SR_FUEL_PID.calculate(BURNER_TEMP_CROSSOVER , TT513_HX504_IN);
BURNER_FUEL_CUT = FCV134_BURNER_FUEL_FLOW_FB + BURNER_FUEL_CUT_OFFSET;
modbusTCPClient1.holdingRegisterWrite(42, BURNER_FUEL_CUT);//write channel 2 (FCV134)
//blower pid
steamGenPID();
//check if out of threshold
if (PT304_TWV308_INPUT_PRESSURE <= 171 && PT304_TWV308_INPUT_PRESSURE >= 169) {
else {
FSM_STATE = STABILIZE_MODE;
case STABILIZE_MODE:
//reformer stabilize
default:
Serial.println("Default.");
}//end switch
}//end if(GRN_BTN_FLAG && !ESTOP_FLAG)
//end loop
void steamGenPID() {
// PT304_TWV308_INPUT_PRESSURE_RAW = modbusTCPClient2.holdingRegisterRead(3023);//ref:43017 read Channel 7 PT304
PT304_TWV308_INPUT_PRESSURE = modbusTCPClient6.inputRegisterRead(6);// read Channel 6 PT304
BLOWER_SPEED_OFFSET = STEAM_GEN_PID.calculate(170 , PT304_TWV308_INPUT_PRESSURE);
Serial.print("BLOWER offset: "); Serial.println(BLOWER_SPEED_OFFSET);
modbusTCPClient1.holdingRegisterWrite(40, BLOWER_SPEED_OFFSET);
void superheatTest() {
if (!modbusTCPClient3.connected()) {
modbusTCPClient3.begin(serverIOEX3, 502);
TT303_HX504_STEAM_OUT = (modbusTCPClient3.holdingRegisterRead(42)) * (0.095); //tt303
TT306_EJECTOR_STEAM_IN = (modbusTCPClient3.holdingRegisterRead(43)) * (0.095); //tt306
RO_PUMP_FEEDBACK = modbusTCPClient6.inputRegisterRead(1);//Ch1 ro water fb
RO_SPEED_OFFSET = SUPER_HEAT_TT303.calc_reverse(130 , TT303_HX504_STEAM_OUT);
modbusTCPClient1.holdingRegisterWrite(41, RO_SPEED_OFFSET);//write channel 1 (WP_Speed)
modbusTCPClient7.coilWrite(10, ON); //WP_EN..Control is opposite
Serial.print("RO_SPEED_OFFSET: "); Serial.println(RO_SPEED_OFFSET);
Serial.print("TT303_HX504_STEAM_OUT: "); Serial.println(TT303_HX504_STEAM_OUT);
Serial.print("TT306_EJECTOR_STEAM_IN: "); Serial.println(TT306_EJECTOR_STEAM_IN);
void connect_IO_Expanders() {
//CONNECT TO ACROMAGS
if (!modbusTCPClient4.connected()) {
modbusTCPClient4.begin(serverIOEX4, 502);
if (!modbusTCPClient5.connected()) {
modbusTCPClient5.begin(serverIOEX5, 502);
if (!modbusTCPClient8.connected()) {
modbusTCPClient8.begin(serverIOEX8, 502);
void readPTs() {
Serial.println("Reading PTs");
//checking PTs
PT318_HX406_OUTPUT_PRESSURE = modbusTCPClient6.inputRegisterRead(3);//read Channel 3 PressureTransducer_318.. 1psi/80counts maximux
PT213_RO_PRESSURE = modbusTCPClient6.inputRegisterRead(4);// read Channel 4 PT213
PT420_STEAM_EJECTOR_PRESSURE = modbusTCPClient6.inputRegisterRead(5);// read Channel 5 PT420
Serial.print("PT318: "); Serial.println(PT318_HX406_OUTPUT_PRESSURE);
Serial.print("PT213: "); Serial.println(PT213_RO_PRESSURE);
Serial.print("PT420: "); Serial.println(PT420_STEAM_EJECTOR_PRESSURE);
Serial.print("PT304: "); Serial.println(PT304_TWV308_INPUT_PRESSURE);
if (PT318_HX406_OUTPUT_PRESSURE >= 240) {
ERROR = 3;
Serial.print("PT318 >240PSI: ");
else {
ERROR = 0;
if ( PT213_RO_PRESSURE >= 240) {
ERROR = 4;
Serial.print("PT213 >240PSI: ");
else {
ERROR = 0;
if (PT420_STEAM_EJECTOR_PRESSURE >= 240) {
ERROR = 5;
Serial.print("PT420 >240PSI: ");
else {
ERROR = 0;
if (PT304_TWV308_INPUT_PRESSURE >= 240) {
ERROR = 6;
Serial.print("PT305 >240PSI: ");
else {
ERROR = 0;
void readTCs() {
//read acromag 4
switch (TC_CHECK_COUNTER) {
case 1:
if (CURRENT_MILLIS - PREVIOUS_MILLIS_3 >= 3000) {
TT142_SR_FUEL = modbusTCPClient3.holdingRegisterRead(40) * (0.095);
TT301_HX406_STEAM_OUT = modbusTCPClient3.holdingRegisterRead(41) * (0.095);
TT306_EJECTOR_STEAM_IN = modbusTCPClient3.holdingRegisterRead(43) * (0.095);
TT313_HX402_STEAM_OUT = modbusTCPClient3.holdingRegisterRead(44) * (0.095);
TT319_HX402_STEAM_SYSTEM = modbusTCPClient3.holdingRegisterRead(45) * (0.095);
TT407_STEAM_REFORMER_OUT_LREF = modbusTCPClient3.holdingRegisterRead(46) * (0.095);
TT408_HTS_IN_LREF = modbusTCPClient3.holdingRegisterRead(47) * (0.095);
if (TT301_HX406_STEAM_OUT > 1000) {
Serial.println("TT301_HX406_STEAM_OUT > 1000C");
ERROR = 13;
if (TT303_HX504_STEAM_OUT > 1000) {
Serial.println("TT303_HX504_STEAM_OUT > 1000C");
ERROR = 14;
if (TT306_EJECTOR_STEAM_IN > 1000) {
Serial.println("TT306_EJECTOR_STEAM_IN > 1000C");
ERROR = 15;
if (TT313_HX402_STEAM_OUT > 1000) {
Serial.println("TT313_HX402_STEAM_OUT > 1000C");
ERROR = 16;
if (TT319_HX402_STEAM_SYSTEM > 1000) {
Serial.println("TT319_HX402_STEAM_SYSTEM > 1000C");
ERROR = 17;
if (TT407_STEAM_REFORMER_OUT_LREF > 1000) {
Serial.println("TT407_STEAM_REFORMER_OUT_LREF > 1000C");
ERROR = 18;
if (TT408_HTS_IN_LREF > 1000) {
Serial.println("TT408_HTS_IN_LREF > 1000C");
ERROR = 19;
Serial.print("TT142_SR_FUEL: ");Serial.println(TT142_SR_FUEL);
Serial.print("TT301_HX406_STEAM_OUT : ");Serial.println(TT301_HX406_STEAM_OUT);
Serial.print("TT303_HX504_STEAM_OUT : ");Serial.println(TT303_HX504_STEAM_OUT);
Serial.print("TT306_EJECTOR_STEAM_IN : ");Serial.println(TT306_EJECTOR_STEAM_IN);
Serial.print("TT313_HX402_STEAM_OUT : ");Serial.println(TT313_HX402_STEAM_OUT);
Serial.print("TT319_HX402_STEAM_SYSTEM : ");Serial.println(TT319_HX402_STEAM_SYSTEM);
Serial.print("TT407_STEAM_REFORMER_OUT_LREF : ");Serial.println(TT407_STEAM_REFORMER_OUT_LREF);
Serial.print("TT408_HTS_IN_LREF : ");Serial.println(TT408_HTS_IN_LREF);
PREVIOUS_MILLIS_3 = millis();
TC_CHECK_COUNTER = 2;
case 2:
//read acromag5
TT410_HTS_OUT_LREF = modbusTCPClient4.holdingRegisterRead(40) * (0.095);
TT411_FPZ_OUT_LREF = modbusTCPClient4.holdingRegisterRead(41) * (0.095);
TT430_SMR_TUBES_INLET = modbusTCPClient4.holdingRegisterRead(42) * (0.095);
TT511_SILICON_CARBIDE_OUT = modbusTCPClient4.holdingRegisterRead(43) * (0.095);
TT512_SILICON_CARBIDE_OUT = modbusTCPClient4.holdingRegisterRead(44) * (0.095);
TT513_HX504_IN = modbusTCPClient4.holdingRegisterRead(45) * (0.095);
TT514_HX504_OUT = modbusTCPClient4.holdingRegisterRead(46) * (0.095);
TT441_SMR_TUBE1_OUT = modbusTCPClient4.holdingRegisterRead(47) * (0.095);
// if (TT410_HTS_OUT_LREF > 1000) {
// Serial.println("TT410_HTS_OUT_LREF > 1000C");
// FSM_STATE = INITIALIZE;
// ERROR = 20;
if (TT411_FPZ_OUT_LREF > 1000) {
Serial.println("TT411_FPZ_OUT_LREF > 1000C");
ERROR = 21;
if (TT430_SMR_TUBES_INLET > 1000) {
Serial.println("TT430_SMR_TUBES_INLET > 1000C");
ERROR = 22;
if (TT511_SILICON_CARBIDE_OUT > 1000) {
Serial.println("TT511_SILICON_CARBIDE_OUT > 1000C");
ERROR = 23;
// if (TT512_SILICON_CARBIDE_OUT > 1000) {
// Serial.println("TT512_SILICON_CARBIDE_OUT > 1000C");
// ERROR = 24;
if (TT513_HX504_IN > 1000) {
Serial.println("TT513_HX504_IN > 1000C");
ERROR = 25;
if (TT514_HX504_OUT > 1000) {
Serial.println("TT514_HX504_OUT > 1000C");
ERROR = 26;
if (TT441_SMR_TUBE1_OUT > 800) {
Serial.println("TT441_SMR_TUBE1_OUT > 1000C");
ERROR = 27;
Serial.print("TT410_HTS_OUT_LREF : ");Serial.println(TT410_HTS_OUT_LREF);
Serial.print("TT411_FPZ_OUT_LREF : ");Serial.println(TT411_FPZ_OUT_LREF);
Serial.print("TT430_SMR_TUBES_INLET : ");Serial.println(TT430_SMR_TUBES_INLET);
Serial.print("TT511_SILICON_CARBIDE_OUT : ");Serial.println(TT511_SILICON_CARBIDE_OUT);
Serial.print("TT512_SILICON_CARBIDE_OUT : ");Serial.println(TT512_SILICON_CARBIDE_OUT);
Serial.print("TT513_HX504_IN : ");Serial.println(TT513_HX504_IN);
Serial.print("TT514_HX504_OUT : ");Serial.println(TT514_HX504_OUT);
Serial.print("TT441_SMR_TUBE1_OUT : ");Serial.println(TT441_SMR_TUBE1_OUT);
TC_CHECK_COUNTER = 3;
case 3:
TT442_SMR_TUBE2_OUT = modbusTCPClient5.holdingRegisterRead(40) * (0.095);
TT443_SMR_TUBE3_OUT = modbusTCPClient5.holdingRegisterRead(41) * (0.095);
TT444_SMR_TUBE4_OUT = modbusTCPClient5.holdingRegisterRead(42) * (0.095);
TT445_SMR_TUBE5_OUT = modbusTCPClient5.holdingRegisterRead(43) * (0.095);
TT446_SMR_TUBE6_OUT = modbusTCPClient5.holdingRegisterRead(44) * (0.095);
TT447_SMR_TUBE7_OUT = modbusTCPClient5.holdingRegisterRead(45) * (0.095);
TT448_SMR_TUBE8_OUT = modbusTCPClient5.holdingRegisterRead(46) * (0.095);
TT449_SMR_TUBE9_OUT = modbusTCPClient5.holdingRegisterRead(47) * (0.095);
if (TT442_SMR_TUBE2_OUT > 800) {
Serial.println("TT442_SMR_TUBE2_OUT > 1000C");
ERROR = 28;
if (TT443_SMR_TUBE3_OUT > 800) {
Serial.println("TT443_SMR_TUBE3_OUT > 1000C");
ERROR = 29;
if (TT444_SMR_TUBE4_OUT > 800) {
Serial.println("TT444_SMR_TUBE4_OUT > 700C");
ERROR = 30;
if (TT445_SMR_TUBE5_OUT > 800) {
Serial.println("TT445_SMR_TUBE5_OUT > 700C");
ERROR = 31;
if (TT446_SMR_TUBE6_OUT > 800) {
Serial.println("TT446_SMR_TUBE6_OUT > 700C");
ERROR = 32;
if (TT447_SMR_TUBE7_OUT > 800) {
Serial.println("TT447_SMR_TUBE7_OUT > 700C");
ERROR = 33;
if (TT448_SMR_TUBE8_OUT > 800) {
Serial.println("TT448_SMR_TUBE8_OUT > 700C");
ERROR = 34;
if (TT449_SMR_TUBE9_OUT > 800) {
Serial.println("TT449_SMR_TUBE9_OUT > 700C");
ERROR = 35;
Serial.print("TT442_SMR_TUBE2_OUT : ");Serial.println(TT442_SMR_TUBE2_OUT);
Serial.print("TT443_SMR_TUBE3_OUT : ");Serial.println(TT443_SMR_TUBE3_OUT);
Serial.print("TT444_SMR_TUBE4_OUT : ");Serial.println(TT444_SMR_TUBE4_OUT);
Serial.print("TT445_SMR_TUBE5_OUT : ");Serial.println(TT445_SMR_TUBE5_OUT);
Serial.print("TT446_SMR_TUBE6_OUT : ");Serial.println(TT446_SMR_TUBE6_OUT);
Serial.print("TT447_SMR_TUBE7_OUT : ");Serial.println(TT447_SMR_TUBE7_OUT);
Serial.print("TT448_SMR_TUBE8_OUT : ");Serial.println(TT448_SMR_TUBE8_OUT);
Serial.print("TT449_SMR_TUBE9_OUT : ");Serial.println(TT449_SMR_TUBE9_OUT);
TC_CHECK_COUNTER = 1;
DB_TX();
void readOut() {
lcd.setBacklight(HIGH);
switch (READOUT_COUNTER) {
case 1:
if (CURRENT_MILLIS - PREVIOUS_MILLIS_4 >= 3000) {
lcd.clear();
lcd.setCursor(0, 0);
lcd.print("P1_");
lcd.print((int)PT304_TWV308_INPUT_PRESSURE);//nine tubes
lcd.setCursor(7, 0);
lcd.print("P2_");
lcd.print((int)PT318_HX406_OUTPUT_PRESSURE);//nine tubes
lcd.setCursor(14, 0);
lcd.print(FSM_STATE);
lcd.setCursor(0, 1);
lcd.print("P3_");
lcd.print((int)PT420_STEAM_EJECTOR_PRESSURE);//nine tubes
lcd.setCursor(7, 1);
lcd.print("P4_");
lcd.print((int)PT213_RO_PRESSURE);//nine tubes
READOUT_COUNTER = 2;
PREVIOUS_MILLIS_4 = millis();
case 2:
lcd.clear();
lcd.print("S9_");
lcd.print((int)TT449_SMR_TUBE9_OUT);//nine tubes
lcd.print("H1_");
lcd.print((int)TT511_SILICON_CARBIDE_OUT);//nine tubes
lcd.print("H2_");
lcd.print((int)TT513_HX504_IN);//nine tubes
lcd.print("SH_");
lcd.print((int)TT301_HX406_STEAM_OUT);//nine tubes
READOUT_COUNTER = 3;
case 3:
lcd.begin(16, 2);
lcd.clear();
lcd.print("S1_");
lcd.print((int)TT441_SMR_TUBE1_OUT);//nine tubes
lcd.print("S2_");
lcd.print((int)TT442_SMR_TUBE2_OUT);//nine tubes
lcd.print("S3_");
lcd.print((int)TT443_SMR_TUBE3_OUT);//nine tubes
lcd.print("S4_");
lcd.print((int)TT444_SMR_TUBE4_OUT);//nine tubes
READOUT_COUNTER = 4;
case 4:
lcd.clear();
lcd.print("S5_");
lcd.print((int)TT445_SMR_TUBE5_OUT);//nine tubes
lcd.print("S6_");
lcd.print((int)TT446_SMR_TUBE6_OUT);//nine tubes
lcd.print("S7_");
lcd.print((int)TT447_SMR_TUBE7_OUT);//nine tubes
lcd.print("S8_");
lcd.print((int)TT448_SMR_TUBE8_OUT);//nine tubes
READOUT_COUNTER = 1;
void integrityCheck() {
while (!modbusTCPClient1.connected()) {
Serial.println("CONNECTING IOEX1.");
while (!modbusTCPClient2.connected()) {
Serial.println("CONNECTING IOEX2.");
while (!modbusTCPClient3.connected()) {
Serial.println("CONNECTING IOEX3.");
while (!modbusTCPClient4.connected()) {
Serial.println("CONNECTING IOEX4.");
while (!modbusTCPClient5.connected()) {
Serial.println("CONNECTING IOEX5.");
while (!modbusTCPClient7.connected()) {
Serial.println("CONNECTING IOEX7.");
while (!modbusTCPClient8.connected()) {
Serial.println("CONNECTING IOEX8.");
while (!modbusTCPClient6.connected()) {
Serial.println("CONNECTING IOEX6.");
PT318_HX406_OUTPUT_PRESSURE = modbusTCPClient6.inputRegisterRead(3);// read Channel 3 PressureTransducer_318.. 1psi/80counts maximum
PT420_STEAM_EJECTOR_PRESSURE = modbusTCPClient6.inputRegisterRead(5);//read Channel 5 PT420
ERROR = 3;
else {
ERROR = 0;
if (PT213_RO_PRESSURE >= 240) {
ERROR = 4;
else {
ERROR = 0;
ERROR = 5;
else {
ERROR = 0;
ERROR = 6;
else {
ERROR = 0;
//analog outputs
modbusTCPClient1.holdingRegisterWrite(41, OFF); //write channel 1 (WP_Speed)
modbusTCPClient1.holdingRegisterWrite(42, OFF); //write channel 2 (FCV134)
modbusTCPClient1.holdingRegisterWrite(43, OFF); //write channel 3 (FCV205)
modbusTCPClient2.holdingRegisterWrite(40, OFF); //write channel 0 (FCV141)
//digital outputs
modbusTCPClient7.coilWrite(5, OFF); //XV801
modbusTCPClient7.coilWrite(9, 1); //BLWR_EN ON bc opposite
modbusTCPClient7.coilWrite(10, 1); //WP_EN ON bc opposite
modbusTCPClient7.coilWrite(2, OFF); //xv909
FCV134_BURNER_FUEL_FLOW_FB = modbusTCPClient6.inputRegisterRead(7);// read Channel 7 FCV134
if (!(FCV134_BURNER_FUEL_FLOW_FB < 10 )) {
ERROR = 2;
SENSOR_INTEGRITY_CHECK = false;
else {
modbusTCPClient1.holdingRegisterWrite(40, 0); //write channel 0 (BLWRSpeed) off
//get that dang dynamic pressure switch off!!
BLOWER_SPEED_FEEDBACK = modbusTCPClient6.holdingRegisterRead(0) * (.001); //10volts/10000counts
while (BLOWER_SPEED_FEEDBACK > 10) {
BLOWER_SPEED_FEEDBACK = modbusTCPClient6.holdingRegisterRead(0) * (.001); //10volts/20000counts
delay(1);
void readOCI() {
// Serial.println("Reading OCI417.");
OCI_RESULT = NODE.readInputRegisters(OCI_INPUT_STATUS_REGISTER, 2); //address,qty
//do something with data if read is successful
if (OCI_RESULT == NODE.ku8MBSuccess)
OCI_INPUT_STATUS_WORD = NODE.getResponseBuffer(0);
// Serial.print("OCI INPUT WORD: ");Serial.println(OCI_INPUT_STATUS_WORD,BIN);
COMBUSTION_PRESSURE_SWITCH = bitRead(OCI_INPUT_STATUS_WORD, 7); //COMBUSTION AIR SW
OCI_OUTPUT_STATUS_WORD = NODE.getResponseBuffer(1);
//Serial.print("OCI OUTPUT WORD: ");Serial.println(OCI_OUTPUT_STATUS_WORD,BIN);
BMM_PROOF_OF_FLAME = bitRead(OCI_OUTPUT_STATUS_WORD, 0);
if (FSM_STATE > BMM_IGNITION && BMM_PROOF_OF_FLAME == false) {
ERROR = 10;
BMM_ALARM_STATUS = bitRead(OCI_OUTPUT_STATUS_WORD, 1);
if (FSM_STATE > BMM_IGNITION && BMM_ALARM_STATUS == true) {
ERROR = 10;
//OCI_TO_BMM_COM=bitRead(OCI_OUTPUT_STATUS_WORD,2);
// if(FSM_STATE>6 && OCI_TO_BMM_COM==true){FSM_STATE=0;ERROR=10;}
void readBtn() {
//read if there has been a change for the inputs
//function for reading buttons and signaling indicators
//check status of inputs xor last di status woth current di status
CURRENT_DI_STATUS_WORD = modbusTCPClient8.inputRegisterRead(48);
DUN_PSL = bitRead(CURRENT_DI_STATUS_WORD, 4);
if (DUN_PSL) {
ERROR = 36;
DUN_PSH = bitRead(CURRENT_DI_STATUS_WORD, 3);
if (DUN_PSH) {
ERROR = 37;
DUN_ZSL = bitRead(CURRENT_DI_STATUS_WORD, 5);
if (!DUN_ZSL && FSM_STATE > BMM_IGNITION) {
ERROR = 38;
DI_STATUS_CHANGE = CURRENT_DI_STATUS_WORD ^ LAST_DI_STATUS_WORD; //xor to check for a change in inputs
Serial.print("CURRENT_DI_STATUS_WORD: "); Serial.println(CURRENT_DI_STATUS_WORD);
Serial.print("DI_STATUS_CHANGE: "); Serial.println(DI_STATUS_CHANGE);
LAST_DI_STATUS_WORD = CURRENT_DI_STATUS_WORD;
if (DI_STATUS_CHANGE ) { //check for a change in inputs
//estop
if (bitRead(DI_STATUS_CHANGE, 0)) {
if (bitRead(CURRENT_DI_STATUS_WORD, 0)) { //estop
ESTOP_FLAG = true; GRN_BTN_FLAG = false; AMB_BTN_FLAG = false; ERROR = 1;
modbusTCPClient7.coilWrite(0, OFF); //green pilot OFF
modbusTCPClient7.coilWrite(0, OFF); //AMB pilot OFF
else {
ESTOP_FLAG == false;
if (ESTOP_FLAG == false) {
//amb button
if (bitRead(DI_STATUS_CHANGE, 2)) {
if (bitRead(CURRENT_DI_STATUS_WORD, 2) && FSM_STATE == STABILIZE_MODE) {
AMB_BTN_FLAG = true;
//modbusTCPClient7.coilWrite(0,0);//grn pilot light
modbusTCPClient7.coilWrite(7, 1); //twv901 switch reformate to PSA
modbusTCPClient7.coilWrite(1, 1); //amb pilot light ON
else {}
//grn btn
if (bitRead(DI_STATUS_CHANGE, 1)) {
if (bitRead(CURRENT_DI_STATUS_WORD, 1)) {
GRN_BTN_FLAG = true;
modbusTCPClient7.coilWrite(0, 1); //grn pilot
//modbusTCPClient7.coilWrite(2,0);//amb pilot
void error_Checker() {
//may be redundant but for safety
//shut gas down if an issue
if (ERROR) {
Serial.println("ERROR CHECKER TRIGGERED!");
GRN_BTN_FLAG = false; AMB_BTN_FLAG = false; ESTOP_FLAG = true;
modbusTCPClient1.holdingRegisterWrite(40, OFF); //write channel 4 (FCV141)
else {
ESTOP_FLAG = false;
void steamPressureLow() {
void monitor_SR_Tube_Temps() {
void blinkGRN() {
if (CURRENT_MILLIS - PREVIOUS_MILLIS_5 >= 500 && GRN_BTN_FLAG == false && ESTOP_FLAG == false) {
PREVIOUS_MILLIS_5 = millis();
if (GRN_PLT_STATE == false) {
GRN_PLT_STATE = true;
else {
GRN_PLT_STATE = false;
modbusTCPClient7.coilWrite(0, GRN_PLT_STATE); //grn pilot
void blinkAMB() {
if (CURRENT_MILLIS - PREVIOUS_MILLIS_6 >= 500 && AMB_BTN_FLAG == false && ESTOP_FLAG == false) {
PREVIOUS_MILLIS_6 = millis();
if (AMB_PLT_STATE == false) {
AMB_PLT_STATE = true;
else {
AMB_PLT_STATE = false;
modbusTCPClient7.coilWrite(1, AMB_PLT_STATE); //grn pilot
void DB_RX() {
/*regRX = telGetValue(TEL_ADDR, REGRX);
if (regRX) {
telWriteValue(TEL_ADDR, REGRX, 0x00);
SUPERHEAT_TIMER = telGetValue(TEL_ADDR, SHTMR);
BMM_OFF_TIMER = telGetValue(TEL_ADDR, BOTMR);
BMM_START_TIMER = telGetValue(TEL_ADDR, BSTMR);
BMM_PURGE_TIMER = telGetValue(TEL_ADDR, BPTMR);
BMM_IGNITION_TIMER = telGetValue(TEL_ADDR, BCTMR);
BURNER_RAMP_TIMER = telGetValue(TEL_ADDR, BRTMR);
BURNER_REACH_END_TIMER = telGetValue(TEL_ADDR, BETMR);
STEAM_GENERATION_TIMER = telGetValue(TEL_ADDR, SGTMR);
STEAM_AT_170PSI_TIMER = telGetValue(TEL_ADDR, SPTMR);
OPEN_SR_FUEL_TIMER = telGetValue(TEL_ADDR, SRTMR);
BLOWER_PURGE_SPEED = telGetValue(TEL_ADDR, BLPSD);
BLOWER_IGNITION_SPEED = telGetValue(TEL_ADDR, BLISD);
BLOWER_RAMP_END = telGetValue(TEL_ADDR, BLEND);
BLOWER_TOP_SPEED = telGetValue(TEL_ADDR, BLTSD);
RO_PUMP_AT_10_GRAMS_PER_SEC = telGetValue(TEL_ADDR, WP10G);
RO_PUMP_TOP_SPEED = telGetValue(TEL_ADDR, WPTSD);
FCV205_AT_35_PERCENT = telGetValue(TEL_ADDR, F205S);
FCV205_AT_50_PERCENT = telGetValue(TEL_ADDR, F205E);
FCV134_BURNER_FUEL_FLOW_IGNITION = telGetValue(TEL_ADDR, BFIGN);
FCV134_BURNER_FUEL_FLOW_RAMP_END = telGetValue(TEL_ADDR, BFRED);
FCV141_SR_FUEL_START_PERCENT = telGetValue(TEL_ADDR, SRFST);
FT132_PIPE_DIA_CONV = telGetValue(TEL_ADDR, FTDIA);
FT132_COUNTS_TO_G_PER_SEC = telGetValue(TEL_ADDR, FTGPS);
FT132_4MA_OFFSET = telGetValue(TEL_ADDR, FT4MA);
BURNER_TEMP_RAMP_END = telGetValue(TEL_ADDR, BTRED);
BURNER_TEMP_CROSSOVER = telGetValue(TEL_ADDR, BTCOV);
SR_FUEL_CUT = telGetValue(TEL_ADDR, SRFCT);
void DB_TX() {
//motor fb,flow fb,fcv position fb
telWriteValue(TEL_ADDR, BL_FB, BLOWER_SPEED_FEEDBACK);
telWriteValue(TEL_ADDR, WP_FB, RO_PUMP_FEEDBACK);
telWriteValue(TEL_ADDR, BF_FB, FCV134_BURNER_FUEL_FLOW_FB);
telWriteValue(TEL_ADDR, SR_FB, FT132_ADJUSTED_MEASURE);
//pressure transducers
telWriteValue(TEL_ADDR, PT213, PT213_RO_PRESSURE);
telWriteValue(TEL_ADDR, PT318, PT318_HX406_OUTPUT_PRESSURE);
telWriteValue(TEL_ADDR, PT420, PT420_STEAM_EJECTOR_PRESSURE);
telWriteValue(TEL_ADDR, PT304, PT304_TWV308_INPUT_PRESSURE);
//thermocouples
telWriteValue(TEL_ADDR, TT142, TT142_SR_FUEL);
telWriteValue(TEL_ADDR, TT301, TT301_HX406_STEAM_OUT);
telWriteValue(TEL_ADDR, TT303, TT303_HX504_STEAM_OUT);
telWriteValue(TEL_ADDR, TT306, TT306_EJECTOR_STEAM_IN);
telWriteValue(TEL_ADDR, TT313, TT313_HX402_STEAM_OUT);
telWriteValue(TEL_ADDR, TT319, TT319_HX402_STEAM_SYSTEM);
telWriteValue(TEL_ADDR, TT407, TT407_STEAM_REFORMER_OUT_LREF);
telWriteValue(TEL_ADDR, TT408, TT408_HTS_IN_LREF);
telWriteValue(TEL_ADDR, TT410, TT410_HTS_OUT_LREF);
telWriteValue(TEL_ADDR, TT411, TT411_FPZ_OUT_LREF);
telWriteValue(TEL_ADDR, TT430, TT430_SMR_TUBES_INLET);
telWriteValue(TEL_ADDR, TT511, TT511_SILICON_CARBIDE_OUT);
telWriteValue(TEL_ADDR, TT512, TT512_SILICON_CARBIDE_OUT);
telWriteValue(TEL_ADDR, TT513, TT513_HX504_IN);
telWriteValue(TEL_ADDR, TT514, TT514_HX504_OUT);
telWriteValue(TEL_ADDR, TT441, TT441_SMR_TUBE1_OUT);
telWriteValue(TEL_ADDR, TT442, TT442_SMR_TUBE2_OUT);
telWriteValue(TEL_ADDR, TT443, TT443_SMR_TUBE3_OUT);
telWriteValue(TEL_ADDR, TT444, TT444_SMR_TUBE4_OUT);
telWriteValue(TEL_ADDR, TT445, TT445_SMR_TUBE5_OUT);
telWriteValue(TEL_ADDR, TT446, TT446_SMR_TUBE6_OUT);
telWriteValue(TEL_ADDR, TT447, TT447_SMR_TUBE7_OUT);
telWriteValue(TEL_ADDR, TT448, TT448_SMR_TUBE8_OUT);
telWriteValue(TEL_ADDR, TT449, TT449_SMR_TUBE9_OUT);
//oci to bmm interface
telWriteValue(TEL_ADDR, OCIIN, OCI_INPUT_STATUS_WORD);
telWriteValue(TEL_ADDR, OCIOT, OCI_OUTPUT_STATUS_WORD);*/
void DB_INIT() {
telWriteValue(TEL_ADDR, REGRX, regRX);
telWriteValue(TEL_ADDR, SHTMR, SUPERHEAT_TIMER);
telWriteValue(TEL_ADDR, BOTMR, BMM_OFF_TIMER);
telWriteValue(TEL_ADDR, BSTMR, BMM_START_TIMER);
telWriteValue(TEL_ADDR, BPTMR, BMM_PURGE_TIMER);
telWriteValue(TEL_ADDR, BCTMR, BMM_IGNITION_TIMER);
telWriteValue(TEL_ADDR, BRTMR, BURNER_RAMP_TIMER);
telWriteValue(TEL_ADDR, BETMR, BURNER_REACH_END_TIMER);
telWriteValue(TEL_ADDR, SGTMR, STEAM_GENERATION_TIMER);
telWriteValue(TEL_ADDR, SPTMR, STEAM_AT_170PSI_TIMER);
telWriteValue(TEL_ADDR, SRTMR, OPEN_SR_FUEL_TIMER);
telWriteValue(TEL_ADDR, BLPSD, BLOWER_PURGE_SPEED);
telWriteValue(TEL_ADDR, BLISD, BLOWER_IGNITION_SPEED);
telWriteValue(TEL_ADDR, BLEND, BLOWER_RAMP_END);
telWriteValue(TEL_ADDR, BLTSD, BLOWER_TOP_SPEED);
telWriteValue(TEL_ADDR, WP10G, RO_PUMP_AT_10_GRAMS_PER_SEC);
telWriteValue(TEL_ADDR, WPTSD, RO_PUMP_TOP_SPEED);
telWriteValue(TEL_ADDR, F205S, FCV205_AT_35_PERCENT);
telWriteValue(TEL_ADDR, F205E, FCV205_AT_50_PERCENT);
telWriteValue(TEL_ADDR, BFIGN, FCV134_BURNER_FUEL_FLOW_IGNITION);
telWriteValue(TEL_ADDR, BFRED, FCV134_BURNER_FUEL_FLOW_RAMP_END);
telWriteValue(TEL_ADDR, SRFST, FCV141_SR_FUEL_START_PERCENT);
telWriteValue(TEL_ADDR, FTDIA, FT132_PIPE_DIA_CONV);
telWriteValue(TEL_ADDR, FTGPS, FT132_COUNTS_TO_G_PER_SEC);
telWriteValue(TEL_ADDR, FT4MA, FT132_4MA_OFFSET);
telWriteValue(TEL_ADDR, BTRED, BURNER_TEMP_RAMP_END);
telWriteValue(TEL_ADDR, BTCOV, BURNER_TEMP_CROSSOVER);
telWriteValue(TEL_ADDR, SRFCT, SR_FUEL_CUT);
void preTransmission() {
digitalWrite(MAX485_RE_NEG, 1);
digitalWrite(MAX485_DE, 1);
void postTransmission() {