Input voltage range for voltage regulator
This regulator is used to obtain a 3V3 output voltage. http://datasheet.elcodis.com/pdf2/78/81/788153/ld1117axx.pdf
What is the acceptable input voltage range for this regulator? I cannot get a clear answer from the datasheet. Would using an DC input of 12V,1.5A be safe? Can someone advise?
If you supply it with 12V, it's going to run pretty hot. (12V - 3.3V) x current draw = watts of power dissipated as heat by the part.
Page 5 shows an Absolute Max of 15V and Power Dissipation 12W. 12W > 8.7V * 1A, so you 'could' run the part at full rated current of 1A IF you had one big-as* properly thermally connected heat sink attached to dissipate 8.7W.
Page 9 shows characteristics with various of Vin: 5.3V, 4.75V to 8V, <10V, Vi - Vo of 5V, and Vi - Vo of 3V.
If you do input 12V, you're outside of what's been characterized.
According to the datasheet you reference, section 5, Vi (input voltage) is spec'd at 10v max. and the dropout voltage (max) is 1.3v at 1A so for 3.3 volts output, the minimum input voltage would be 3.3 + 1.3 = 4.6 volts. Recognize that needs to take into account any dips in the supply due to ripple - if the low point of any ripple falls below 4.6, you are likely to see that start showing up on the output.
gpsmikey:
The maximum rating is at 15V. Does it mean it is ok to supply DC 12V? Most DC jacks are 12V today.
CrossRoads:
This is right. However, the maximum rating is 15V. So, I guess it should be able to take the heat.
Where do you find 20 volts for the input? The section I was looking at listed "Vi" Operating input voltage at 100ma as 10v in the "Max" column (about in the middle of the table there for section 5) In section 3, under "Absolute Maximum Ratings" it lists the input as 15v. Personally, I tend to stay away from "Absolute Maximum" ratings and within the bounds listed under the normal specs (and still stay away from the edges). Too many years working with avionics design to go near the edges of the specs. :o
gpsmikey:
Sorry. I was reading from another similar datasheet. It should be 15V, not 20V. My mistake.