There is no surprise that you have not found the desired relay. What is the purpose? Please show a schematic of the circuit you need to switch with a relay. Perhaps there is a better way.
Relay contacts will always arc, AC or DC. DC will give bigger arcs. An inductive load at DC may arc forever if the inductive reverse voltage is not controlled.
Switching a high DC voltage may require a vacuum relay. None will work at 5 volts.
Is is possible for me to use the 240VAC switching relay or is there a risk of the contacts arcing?
Any guidance would be most appreciated!
Thanks
The problem you will have is you are looking to switch 450 VDC with what amounts to a negligible current. The relay contacts will need something like a silver plate. Then a 5 volt coil adds to finding something reasonably priced. On the bright side you are switching a very low current. What is your load, inductive or resistive?
Maybe you can find a DC SSR but even a 500 VDC 7.0 amp SSR is overkill and with an SSR you need to consider leakage current.
The load is a 90k resistor across 450VDC. This is to create a load of 5mA max, controlled on/off with a relay.The purpose is to simulate a current drain on a electric car battery. There are a bank of resistors with values greater than 90k also to simulate 1mA to 5mA.
balgill021:
Thanks
So a resistive load only! Are you switching the ground end or the hot end?
Look for an OPEN FRAME relay with the armature isolated from the contacts so you can wire directly to the contacts, not using any built-in wiring. That way you can keep your HV wiring from anything else.
How often do you need switching and are you opening or closing the circuit?
balgill021:
The relay can be in the posituve or ground side. I'm only interested in creating the load by opening and closing the circuit every minute or so.
Thanks
In that case, you can use a cheap 5 volt relay to control a 120 volt industrial type open frame relay to do that HV switching.
balgill021:
Yes there's no reason why a mosfer can't be used. I've never used one to switch 450Vdc before. With a relay at least the coil and contacts can have 1KV+ isolation. I'm unsure what isolation can be acheived with a mosfet unless an opto isolator is used on the gate.
Continuous arcing of DC switches and relays is not related to whether the load is inductive of resistive (although inductive loads cause more damage due to kickback).
The important factor is how much DC voltage and power is available to sustain the arc and how much physical separation is between the contacts. Its easy to make a switch rated at 10A 240Vac that self-quenches, much
harder to do one for 10A 240Vdc - that's a specialist piece of gear called a DC contactor.
450V / 5mA means only about a watt is available to sustain the arc current through the resistor, not enough to be a problem I think.
That 10A at 240Vdc switch/contactor has several kilowatts available to sustain an arc, a completely different realm.
Very low voltages are usually safe even with very high currents as a certain amount of voltage is needed to ionize air reliably.
Most standard mains switches rated for 240Vac will typically be rated for only 24Vdc as the safe current limit drops rapidly with increasing voltage. I've seen a single solar panel hold a significant sized arc in bright sun for instance, at only about 36V.
I think the video does a nice job using AC and DC with a simple resistive heater load. While the thread starter is hardly concerned with something like this for some it may be worth saving.
Do you really need isolation? You said (implied?) that one side is grounded. I'm assuming that someone who is messing with car batteries already has a good handle on safety. The resistor automatically limits the amount of current from +450V, and is mostly non-inductive so there's not much back EMF.