Replacing UPS 9Ah with 105Ah

I have seen it done. It does work. But you ahve the correct thought of taking it out, testing-using the battery. The problems ive have seen are ,

  1. the charging system of the UPS wasnt ment for that kind load to recharge
  2. the ( even thought it will be outside of it) parts arent ment to be around the off gas of the wet cell battery
  3. the UPS Heat sink and regulaters were kinda designed around the shorter power outages (15min type)
    Those are what ive ran into.