Current Status
//this is for pcb revision3 with acromags
//Had to change some of the digital outputs for the new PCB
//need to figure out digital inputs for the
//green amber and estop buttons.
//As far as the BMM.ALARM and BMM.POF,
//These can be read on the OCI417.10
#include<SPI.h>
#include<Ethernet.h>
#include<ArduinoModbus.h>
#include<ModbusMaster.h>
#include<EEPROM.h>
#include<pid.h>
//For OCI417 module
#define MAX485_DE 12
#define MAX485_RE_NEG 13
//ECU jibber jabber
#define ESTOP_BREAK 40
#define LED_PWR 22
#define TRACO_24VDC 23
//TIMING PARAMETERS
unsigned long LOOP_TIME;
unsigned long CURRENT_MILLIS=0;//used to keep track of time
unsigned long PREVIOUS_MILLIS=0;//used to keep track of time
unsigned long PREVIOUS_MILLIS_1=0;//used in case 8
unsigned long PREVIOUS_MILLIS_2=0;//used in case 7
unsigned long PREVIOUS_MILLIS_3=0;//used in readTCs function
unsigned long LOOP_MILLIS=0;//used to caluclate loop function time.
//timing constants
const long SUPERHEAT_TIMER=50000;
const int BMM_OFF_TIMER=30000;
const int BMM_START_TIMER=5000;
const int BMM_PURGE_TIMER=32000;
const long BMM_IGNITION_TIMER=30000;
const long BURNER_RAMP_TIMER=240000;//4mins
const long BURNER_REACH_815C=1200000;//SECONDS//20mins
const long STEAM_GENERATION_TIMER=1800000;//30 mins
const int STEAM_AT_170PSI_TIMER=10000;//gwrgw
const int OPEN_SR_FUEL_TIMER=180000;//3 mins
//superheat delta constant PARAMETERS
const int SUPERHEAT_DELTA_CONSTANT=0.3;// ~3degreesC per 10ms
uint16_t PREVIOUS_TT407=0,PREVIOUS_TT408=0;
//counter
uint8_t TC_CHECK_COUNTER=1;
//BLOWER VARIABLES
const int BLOWER_PURGE_SPEED=4, BLOWER_IGNITION_SPEED=3407,BLOWER_RAMP_END=7150;//2 to keep the dps triggered .17 * 20043counts
uint16_t BLOWER_SPEED_AT_170PSI,BLOWER_SPEED_FEEDBACK=0,BLOWER_CALCULATE_SPEED;//feedback in counts
bool BLOWER_ENABLE=false;
//RO PUMP VARIABLES
const int MAX_RO_PRESSURE=250;//psi
const int RO_PUMP_AT_10_GRAMS_PER_SEC=2500;//counts
uint8_t RO_PUMP_SPEED_COMMANDED=0,RO_PUMP_FEEDBACK=0;
bool RO_PUMP_ENABLE=false;
//FLOW CONTROL VALVES
uint8_t FCV205_HX406_INLET_FLOW=0;//g/sec
uint16_t FCV134_BURNER_FUEL_FLOW_FB;//counts
const int FCV134_BURNER_FUEL_FLOW_IGNITION=10079,FCV134_BURNER_FUEL_FLOW_RAMP_END=15320;//5 volts ~40 percent open
uint8_t FCV141_SR_FEED_FLOW=0;//PERCENTAGE
uint8_t FT132_NG_FEED_FLOW=0; // UNSURE OF UNITS??
bool TWV308_STEAM_REFORMER_FEED=false;//NEED TO DETERMINE DIRECTIONS
bool TWV901_LOW_PRESSURE_REFORMATE=false;//NEED TO DETERMINE SIRECTIONS
uint8_t ATMOSPHERIC_PRESSURE=5;//psi
//INITIALIZE PRESSURE TRANSDUCER VARIABLES
uint16_t PT213_RO_PRESSURE,PT318_HX406_OUTPUT_PRESSURE;//psi
uint16_t PT420_STEAM_EJECTOR_PRESSURE,PT304_TWV308_INPUT_PRESSURE;//psi
//INITIALIZE THERMOCOUPLE VARIABLES
uint16_t TT142_SR_FUEL,TT301_HX406_STEAM_OUT,TT303_HX504_STEAM_OUT,TT306_EJECTOR_STEAM_IN;
uint16_t TT313_HX402_STEAM_OUT,TT319_HX402_STEAM_SYSTEM,TT407_STEAM_REFORMER_OUT_LREF;
uint16_t TT408_HTS_IN_LREF,TT410_HTS_OUT_LREF,TT411_FPZ_OUT_LREF,TT430_SMR_TUBES_INLET;
uint16_t TT511_SILICON_CARBIDE_OUT,TT512_SILICON_CARBIDE_OUT,TT513_HX504_IN,TT514_HX504_OUT;
uint16_t TT441_SMR_TUBE1_OUT,TT442_SMR_TUBE2_OUT,TT443_SMR_TUBE3_OUT,TT444_SMR_TUBE4_OUT;
uint16_t TT445_SMR_TUBE5_OUT,TT446_SMR_TUBE6_OUT,TT447_SMR_TUBE7_OUT,TT448_SMR_TUBE8_OUT;
uint16_t TT449_SMR_TUBE9_OUT;
unit16_t HOLD_BURNER_TEMP;
//OCI417 MODBUS PARAMETERS
const int OCI_INPUT_STATUS_REGISTER=25;
const int OCI_OUTPUT_STATUS_REGISTER=26;
const int OCI_UNIT_ID=1;
uint16_t OCI_INPUT_STATUS_WORD=0;
uint16_t OCI_OUTPUT_STATUS_WORD=0;
uint8_t OCI_RESULT;
bool COMBUSTION_PRESSURE_SWITCH,BMM_ALARM_STATUS;
bool BMM_PROOF_OF_FLAME,OCI_TO_BMM_COM;
bool DUN_PSH,DUN_PSL,DUN_ZSL;
ModbusMaster NODE;
//FLAGS
bool GRN_BTN_FLAG=false,AMB_BTN_FLAG=false,ESTOP_FLAG=false,SENSOR_INTEGRITY_CHECK=false;
bool WATCHDOG_TIMER_FLAG=false;
bool PSI_INIT_TIMER=false;
uint8_t FSM_STATE=0;
uint8_t ERROR=0;//ERROR 0 means no ERROR.
//Mac Address of controller
byte mac[] = {0xdE,0xAD,0xBE,0xEF,0xED};
//needs to be similar to Acromag because will not connect
IPAddress ip(128,1,1,110);
//PARAMETERS FOR ACROMAG SERVERS
EthernetClient ethClient1;
EthernetClient ethClient2;
EthernetClient ethClient3;
EthernetClient ethClient4;
EthernetClient ethClient5;
EthernetClient ethClient6;
EthernetClient ethClient7;
ModbusTCPClient modbusTCPClient1(ethClient1);
ModbusTCPClient modbusTCPClient2(ethClient2);
ModbusTCPClient modbusTCPClient3(ethClient3);
ModbusTCPClient modbusTCPClient4(ethClient4);
ModbusTCPClient modbusTCPClient5(ethClient5);
ModbusTCPClient modbusTCPClient6(ethClient6);
ModbusTCPClient modbusTCPClient7(ethClient7);
IPAddress serverA1(128,1,1,101); // IP of Acromag1 973EN-4006 analog output
IPAddress serverA2(128,1,1,102); // IP of Acromag2 963EN-4012 analog input
IPAddress serverA3(128,1,1,103); // IP of Acromag3 989EN-4016 digital output
IPAddress serverA4(128,1,1,104); // IP of Acromag4 965EN-4006 tc
IPAddress serverA5(128,1,1,105); // IP of Acromag5 965EN-4006 tc
IPAddress serverA6(128,1,1,106); // IP of Acromag6 965EN-4006 tc
IPAddress serverA7(128,1,1,107); // IP of Acromag7 965EN-4006 tc
//PIDs
//steam gen pid
PID Steam_Gen_PID = PID(0.1, 1, -1, 0.5, 0.01, 0.5);//dt,max,min,kp,kd,ki;//
PID OPEN_SR_FUEL_PID = PID(0.1, 1000, -1000, 0.5, 0.01, 0.5);//dt,max,min,kp,kd,ki;//
uint8_t BLOWER_SPEED_OFFSET;
uint16_t BURNER_FUEL_CUT_OFFSET, BURNER_FUEL_CUT;//for pid in case 9 open sr fuel also case 10
pinMode(MAX485_RE_NEG, OUTPUT);
pinMode(MAX485_DE, OUTPUT);
// Init in receive mode rs485
digitalWrite(MAX485_RE_NEG, 0);
digitalWrite(MAX485_DE, 0);
Serial.begin(9600); // for dedbugging
Serial1.begin(9600);//FOR OCI MODULE rs485
NODE.begin(1, Serial1); //unit id1 on serial1
NODE.preTransmission(preTransmission);
NODE.postTransmission(postTransmission);
delay(500);//wait for system to boot up
pinMode(LED_PWR,OUTPUT);
digitalWrite(LED_PWR,HIGH);
pinMode(TRACO_24VDC,OUTPUT);
digitalWrite(TRACO_24VDC,HIGH);
pinMode(ESTOP_BREAK,OUTPUT);
digitalWrite(ESTOP_BREAK,HIGH);
//reseting wifichip
pinMode(7,OUTPUT);
digitalWrite(7,HIGH);
delay(50);
//start the Ethernet connection and the server:
Ethernet.begin(mac, ip);
//CONNECT TO ACROMAGS
while(!modbusTCPClient1.connected()){modbusTCPClient1.begin(serverA1,502);}
while(!modbusTCPClient2.connected()){modbusTCPClient2.begin(serverA2,502);}
while(!modbusTCPClient3.connected()){modbusTCPClient3.begin(serverA3,502);}
while(!modbusTCPClient4.connected()){modbusTCPClient4.begin(serverA4,502);}
while(!modbusTCPClient5.connected()){modbusTCPClient5.begin(serverA5,502);}
while(!modbusTCPClient6.connected()){modbusTCPClient6.begin(serverA6,502);}
while(!modbusTCPClient7.connected()){modbusTCPClient7.begin(serverA7,502);}
readBtn();
readOCI();
integrityCheck();
modbusTCPClient1.holdingRegisterWrite(0x12,(0));//write channel 0 (BLWRSpeed) off
//get that dang dynamic pressure switch off!!
BLOWER_SPEED_FEEDBACK=modbusTCPClient2.holdingRegisterRead(3016)*(.0005);//10volts/20000counts
while(BLOWER_SPEED_FEEDBACK>0){
delay(1);
CURRENT_MILLIS=millis();//So as to not divide by zero on first looptime.
LOOP_MILLIS=millis();
LOOP_TIME=LOOP_MILLIS-CURRENT_MILLIS;
connect_IO_Expanders();
superheatTest();
Serial.println(FSM_STATE);//debugging
Serial.print("Error:");Serial.println(ERROR);//debugging
readTCs();
readBtn();
readOCI();
readPTs();
if(!SENSOR_INTEGRITY_CHECK){integrityCheck();}
if(DUN_PSL){readOCI();}
switch(FSM_STATE){
case 0: //initialize
Serial.println("In case 0");
if(!SENSOR_INTEGRITY_CHECK){break;}
modbusTCPClient3.coilWrite(4,255);//CH4 digital output xv909
if(!COMBUSTION_PRESSURE_SWITCH){
modbusTCPClient1.holdingRegisterWrite(0x12,(BLOWER_PURGE_SPEED*2000));//write channel 0 (BLWRSpeed)
modbusTCPClient3.coilWrite(13,0);//BLWR_EN..The logic is opposite
break;}
if(!DUN_PSL){Serial.print("Break due to DUN_PSL Switch: ");Serial.println(DUN_PSL);break;}
//check for RO water???
modbusTCPClient1.holdingRegisterWrite(0x12,OFF);//write channel 0 (BLWRSpeed)
modbusTCPClient3.coilWrite(13,255);//BLWR_EN..The logic is opposite
FSM_STATE=1;break;
case 1: //depressurise reformer
Serial.println("In case 1");
modbusTCPClient3.coilWrite(8,OFF);//TWV308
if(PT420_STEAM_EJECTOR_PRESSURE >= ATMOSPHERIC_PRESSURE){
PT420_STEAM_EJECTOR_PRESSURE = (modbusTCPClient2.holdingRegisterRead(3022)*(.0125))-47;//ref:43016 read Channel 6 PT420
// PT420_STEAM_EJECTOR_PRESSURE = modbusTCPClient2.holdingRegisterRead(3022);
modbusTCPClient3.coilWrite(4,OFF);//CH4 digital output xv909
//250 psi
if(PT213_RO_PRESSURE<250){
//just guessing on the fcv205 flow, as long as we stay beneath 250psi
modbusTCPClient1.holdingRegisterWrite(0x12,BLOWER_PURGE_SPEED*2000);//write channel 0 (BLWRSpeed)
modbusTCPClient1.holdingRegisterWrite(0x15,7000);//write channel 3 (FCV205)//made steam at 1000//last 3000//~about 35 percent according to Shawn
modbusTCPClient1.holdingRegisterWrite(0x13,RO_PUMP_AT_10_GRAMS_PER_SEC);//write channel 1 (WP_Speed) made steam at 1*2000//last 3*2000
modbusTCPClient3.coilWrite(14,OFF);//WP_EN..Control is opposite
modbusTCPClient3.coilWrite(13,OFF);//BLWR_EN..Control is opposite
FSM_STATE=2;
PREVIOUS_MILLIS=millis();
case 2://Superheat Test
Serial.println("case 2");
//make sure we are closed//xv909
//monitor tc 407 & 408
//need a timer
if(CURRENT_MILLIS - PREVIOUS_MILLIS <= SUPERHEAT_TIMER){
TT407_STEAM_REFORMER_OUT_LREF=modbusTCPClient5.holdingRegisterRead(3012)*(18.4/265);
TT408_HTS_IN_LREF=modbusTCPClient5.holdingRegisterRead(3013)*(18.4/265);
//guessing on 300 degrees centigrade
if(TT407_STEAM_REFORMER_OUT_LREF >300){
ERROR=7;FSM_STATE=0;break;
if(TT408_HTS_IN_LREF>300){
FSM_STATE=3;
PREVIOUS_MILLIS = millis();
case 3://bmm off //30 secondsconnect_IO_Expanders();
Serial.println("case 3");
if(CURRENT_MILLIS - PREVIOUS_MILLIS <= BMM_OFF_TIMER){
modbusTCPClient3.coilWrite(12,OFF);//BMM_CR2 bmm off
FSM_STATE=4;
modbusTCPClient3.coilWrite(12,255);//BMM_CR2 turn on
case 4://bmm on //5 seconds
Serial.println("Case 4");
if(CURRENT_MILLIS - PREVIOUS_MILLIS <= BMM_START_TIMER){
FSM_STATE=5;
case 5://bmm purge
Serial.println("Case 5");
if(CURRENT_MILLIS - PREVIOUS_MILLIS <= BMM_PURGE_TIMER){
FSM_STATE=6;
case 6://BMM ignition
Serial.println("Case 6");
modbusTCPClient1.holdingRegisterWrite(0x12,BLOWER_IGNITION_SPEED);//write channel 0 (BLWRSpeed)
modbusTCPClient1.holdingRegisterWrite(0x14,FCV134_BURNER_FUEL_FLOW_IGNITION);//write channel 2 (FCV134)
if(CURRENT_MILLIS - PREVIOUS_MILLIS >= BMM_IGNITION_TIMER){
if(!BMM_PROOF_OF_FLAME){ERROR=8;FSM_STATE=0;break;}
else{FSM_STATE=7;PREVIOUS_MILLIS=millis();PREVIOUS_MILLIS_2=millis();break;}
case 7://start burner ramp//15 minutes//900 seconds
Serial.println("Case 7");
//burner ramp is 4mins
//timing to reach 800c is 15 mins
TT511_SILICON_CARBIDE_OUT=(modbusTCPClient5.holdingRegisterRead(3017))*(0.07);
TT513_HX504_IN=(modbusTCPClient6.holdingRegisterRead(3013))*(0.07);
Serial.print("TT511: ");Serial.println(TT511_SILICON_CARBIDE_OUT);
Serial.print("TT513: ");Serial.println(TT513_HX504_IN);
Serial.print("Burner Ramp Timer 15 mins: ");Serial.println(CURRENT_MILLIS - PREVIOUS_MILLIS);
if(CURRENT_MILLIS - PREVIOUS_MILLIS >= BURNER_REACH_815C){
if(TT511_SILICON_CARBIDE_OUT >= 815){
FSM_STATE=8;
if( TT513_HX504_IN >= 815){
FSM_STATE=8;
ERROR=11;FSM_STATE=0;break;
if(TT511_SILICON_CARBIDE_OUT >= 815 ){
FSM_STATE=8;
FSM_STATE=8;
BLOWER_SPEED_FEEDBACK = modbusTCPClient2.holdingRegisterRead(3016);//10volts/20000counts //~3400
FCV134_BURNER_FUEL_FLOW_FB = modbusTCPClient2.holdingRegisterRead(3026);//ref:43028 read Channel 10 FCV134//~10079
Serial.print("Blower FB: ");Serial.println(BLOWER_SPEED_FEEDBACK);
Serial.print("FCV134 FB: ");Serial.println(FCV134_BURNER_FUEL_FLOW_FB);
if(CURRENT_MILLIS - PREVIOUS_MILLIS <= BURNER_RAMP_TIMER){
if(CURRENT_MILLIS - PREVIOUS_MILLIS_2 >= 5000){
//if(BLOWER_SPEED_FEEDBACK<=14030){
//modbusTCPClient1.holdingRegisterWrite(0x12,BLOWER_SPEED_FEEDBACK+220);}//write channel 0 blwr speed//44counts/sec
//if(FCV134_BURNER_FUEL_FLOW_FB<=16121){
//modbusTCPClient1.holdingRegisterWrite(0x14,FCV134_BURNER_FUEL_FLOW_FB+125);}//25counts/sec
modbusTCPClient1.holdingRegisterWrite(0x14,FCV134_BURNER_FUEL_FLOW_RAMP_END);//16121 best thus far, fuel
modbusTCPClient1.holdingRegisterWrite(0x12,BLOWER_RAMP_END);//7100 best thus far, blwr
PREVIOUS_MILLIS_2 = millis();
else{
//modbusTCPClient1.holdingRegisterWrite(0x14,16121);//25counts/sec
//modbusTCPClient1.holdingRegisterWrite(0x12,13000);//write channel 0 blwr speed//44counts/sec
case 8://Steam generation
Serial.println("Case 8");
//steam gen timeout 30 mins
if(CURRENT_MILLIS - PREVIOUS_MILLIS >= STEAM_GENERATION_TIMER){ERROR=9;FSM_STATE=0;break;}
Serial.print("Elapsed Time(time 1800ms): ");Serial.println(CURRENT_MILLIS - PREVIOUS_MILLIS);
//PID control blower to acheive 170PSI pt304
BLOWER_SPEED_FEEDBACK=modbusTCPClient2.holdingRegisterRead(3016);//10volts/20000counts
if(BLOWER_SPEED_FEEDBACK<16000){
BLOWER_SPEED_OFFSET = Steam_Gen_PID.calculate(170 , PT304_TWV308_INPUT_PRESSURE);
BLOWER_CALCULATE_SPEED = BLOWER_SPEED_FEEDBACK + BLOWER_SPEED_OFFSET;
modbusTCPClient1.holdingRegisterWrite(0x12,BLOWER_CALCULATE_SPEED);}//write channel 0 (BLWRSpeed)
if(PT304_TWV308_INPUT_PRESSURE <= 171 && PT304_TWV308_INPUT_PRESSURE >= 169){
if(PSI_INIT_TIMER == false){ PREVIOUS_MILLIS_1 = millis(); PSI_INIT_TIMER = true; }
if(CURRENT_MILLIS - PREVIOUS_MILLIS_1 >= STEAM_AT_170PSI_TIMER){
BLOWER_SPEED_AT_170PSI=BLOWER_SPEED_FEEDBACK;
modbusTCPClient1.holdingRegisterWrite(0x12,BLOWER_SPEED_AT_170PSI*2000);
modbusTCPClient3.coilWrite(5,255);//XV501 ON
FSM_STATE=9; PREVIOUS_MILLIS = millis(); PSI_INIT_TIMER=false; =TT513_HX504_IN; break;
else{PSI_INIT_TIMER=false;}//If not in bounds of 17-psi, reset timer.
case 9://OPEN SR FUEL
Serial.println("Case 9:");
modbusTCPClient3.coilWrite(9,255);//TWV308 ON//channeling right when in front of refromer r050
modbusTCPClient1.holdingRegisterWrite(0x15,10000);//write channel 3 (FCV205)//50 percent
FCV134_BURNER_FUEL_FLOW_FB = (modbusTCPClient2.holdingRegisterRead(3026)*(.005))-20;//ref:43028 read Channel 10 FCV134
if(CURRENT_MILLIS-PREVIOUS_MILLIS<=180000){
BURNER_FUEL_CUT_OFFSET = OPEN_SR_FUEL_PID.calculate(HOLD_BURNER_TEMP , TT513_HX504_IN);
BURNER_FUEL_CUT= FCV134_BURNER_FUEL_FLOW_FB + BURNER_FUEL_CUT_OFFSET;
modbusTCPClient1.holdingRegisterWrite(0x14, BURNER_FUEL_CUT);//write channel 2 (FCV134)
//reset timing if temp falls out of threshold
if((HOLD_BURNER_TEMP>(TT513_HX504_IN+5)) || (HOLD_BURNER_TEMP<(TT513_HX504_IN-5))){PREVIOUS_MILLIS=millis();break;}
else{
if(ERROR==0){FSM_STATE=10;PREVIOUS_MILLIS=millis();break;}
FSM_STATE=9; PREVIOUS_MILLIS=millis();break;
case 10://idle hold mode blower/burner pid
Serial.println("Case 10:");
//3 mins idle
//burner fuel PID
//blower pid
modbusTCPClient1.holdingRegisterWrite(0x12,BLOWER_CALCULATE_SPEED);//write channel 0 (BLWRSpeed)
//check if out of threshold
if(PT304_TWV308_INPUT_PRESSURE <= 171 && PT304_TWV308_INPUT_PRESSURE >= 169){PREVIOUS_MILLIS=millis();break;}
else{FSM_STATE=11;break;}
case 11://reformer stabilize
Serial.println("Case 11:");
default:
Serial.println("Default.");
}//end switch
LOOP_MILLIS = millis();
}//end loop
void superheatTest(){
int DELTA_TT407,DELTA_TT408;
//These dont seem to be changing enough
PREVIOUS_TT407=TT407_STEAM_REFORMER_OUT_LREF;
PREVIOUS_TT408=TT408_HTS_IN_LREF;
if (!modbusTCPClient5.connected()){modbusTCPClient5.begin(serverA5,502);Serial.println("Connecting to A5 for superheat test.");}
TT407_STEAM_REFORMER_OUT_LREF=modbusTCPClient5.holdingRegisterRead(3012)*(18.4/265);//current temp tt408
TT408_HTS_IN_LREF=modbusTCPClient5.holdingRegisterRead(3013)*(18.4/265);//current temp tt408
DELTA_TT407 = (TT407_STEAM_REFORMER_OUT_LREF - PREVIOUS_TT407)/(LOOP_TIME);
DELTA_TT408 = (TT408_HTS_IN_LREF - PREVIOUS_TT408)/(LOOP_TIME);
Serial.print("CURRENT_TT407: ");Serial.println(TT407_STEAM_REFORMER_OUT_LREF);
Serial.print("PREVIOUS_TT407: ");Serial.println(PREVIOUS_TT407);
Serial.print("CURRENT_TT408: ");Serial.println(TT408_HTS_IN_LREF);
Serial.print("PREVIOUS_TT408: ");Serial.println(PREVIOUS_TT408);
Serial.print("CURRENT_MILLIS: ");Serial.println(CURRENT_MILLIS);
Serial.print("LOOP_MILLIS: ");Serial.println(LOOP_MILLIS);
Serial.print("LOOP TIME: ");Serial.println(LOOP_TIME);
Serial.print("DELTA_TT407: ");Serial.println(DELTA_TT407);//debugging
Serial.print("DELTA_TT408: ");Serial.println(DELTA_TT408);//debugging
if(DELTA_TT407 > SUPERHEAT_DELTA_CONSTANT || DELTA_TT408 > SUPERHEAT_DELTA_CONSTANT){
modbusTCPClient1.holdingRegisterWrite(0x13,20000);//write channel 1 (WP_Speed) full speed ahead sire
else{
modbusTCPClient1.holdingRegisterWrite(0x13,RO_PUMP_AT_10_GRAMS_PER_SEC);//write channel 1 (WP_Speed) full speed ahead sire
void connect_IO_Expanders(){
if(!modbusTCPClient1.connected()){modbusTCPClient1.begin(serverA1,502);}
if(!modbusTCPClient2.connected()){modbusTCPClient2.begin(serverA2,502);}
if(!modbusTCPClient3.connected()){modbusTCPClient3.begin(serverA3,502);}
if(!modbusTCPClient4.connected()){modbusTCPClient4.begin(serverA4,502);}
if(!modbusTCPClient5.connected()){modbusTCPClient5.begin(serverA5,502);}
if(!modbusTCPClient6.connected()){modbusTCPClient6.begin(serverA6,502);}
if(!modbusTCPClient7.connected()){modbusTCPClient7.begin(serverA7,502);}
void readPTs() {
Serial.println("Reading PTs");
//checking PTs
PT318_HX406_OUTPUT_PRESSURE = (modbusTCPClient2.holdingRegisterRead(3020)*(.0125))-50;//ref:43017 read Channel 4 PressureTransducer_318.. 1psi/80counts maximux
PT213_RO_PRESSURE =100; //(modbusTCPClient2.holdingRegisterRead(3021)*(.0125))-50;//ref:43028 read Channel 5 PT213
PT304_TWV308_INPUT_PRESSURE = (modbusTCPClient2.holdingRegisterRead(3023)*(.0125))-50;//ref:43017 read Channel 7 PT304
//raw data
//PT318_HX406_OUTPUT_PRESSURE = modbusTCPClient2.holdingRegisterRead(3020);
//PT213_RO_PRESSURE = modbusTCPClient2.holdingRegisterRead(3021);
//PT420_STEAM_EJECTOR_PRESSURE = modbusTCPClient2.holdingRegisterRead(3022);
//PT304_TWV308_INPUT_PRESSURE = modbusTCPClient2.holdingRegisterRead(3023);
Serial.print("PT318: ");Serial.println(PT318_HX406_OUTPUT_PRESSURE);
Serial.print("PT213: ");Serial.println(PT213_RO_PRESSURE);
Serial.print("PT420: ");Serial.println(PT420_STEAM_EJECTOR_PRESSURE);
Serial.print("PT304: ");Serial.println(PT304_TWV308_INPUT_PRESSURE);
if(PT318_HX406_OUTPUT_PRESSURE>=240){FSM_STATE=0;ERROR=3;Serial.print("PT318 >240PSI");Serial.println(PT318_HX406_OUTPUT_PRESSURE);}
else{ERROR=0;}
if(PT213_RO_PRESSURE>=240){FSM_STATE=0;ERROR=4;Serial.print("PT213 >240PSI");Serial.println(PT213_RO_PRESSURE);}
else{ERROR=0;}
if(PT420_STEAM_EJECTOR_PRESSURE>=240){FSM_STATE=0;ERROR=5;Serial.print("PT420 >240PSI");Serial.println(PT420_STEAM_EJECTOR_PRESSURE);}
else{ERROR=0;}
if(PT304_TWV308_INPUT_PRESSURE>=240){FSM_STATE=0;ERROR=6;Serial.print("PT305 >240PSI");Serial.println(PT304_TWV308_INPUT_PRESSURE);}
else{ERROR=0;}
void readTCs(){
TT142_SR_FUEL=modbusTCPClient4.holdingRegisterRead(3012)*(18.4/265);
TT301_HX406_STEAM_OUT=modbusTCPClient4.holdingRegisterRead(3013)*(18.4/265);
TT303_HX504_STEAM_OUT=modbusTCPClient4.holdingRegisterRead(3014)*(18.4/265);
TT306_EJECTOR_STEAM_IN=modbusTCPClient4.holdingRegisterRead(3015)*(18.4/265);
TT313_HX402_STEAM_OUT=modbusTCPClient4.holdingRegisterRead(3016)*(18.4/265);
TT319_HX402_STEAM_SYSTEM=modbusTCPClient4.holdingRegisterRead(3017)*(18.4/265);
TT410_HTS_OUT_LREF=modbusTCPClient5.holdingRegisterRead(3014)*(18.4/265);
TT411_FPZ_OUT_LREF=modbusTCPClient5.holdingRegisterRead(3015)*(18.4/265);
TT430_SMR_TUBES_INLET=modbusTCPClient5.holdingRegisterRead(3016)*(18.4/265);
TT511_SILICON_CARBIDE_OUT=modbusTCPClient5.holdingRegisterRead(3017)*(18.4/265);
TT512_SILICON_CARBIDE_OUT=modbusTCPClient6.holdingRegisterRead(3012)*(18.4/265);
TT513_HX504_IN=modbusTCPClient6.holdingRegisterRead(3013)*(18.4/265);
TT514_HX504_OUT=modbusTCPClient6.holdingRegisterRead(3014)*(18.4/265);
TT441_SMR_TUBE1_OUT=modbusTCPClient6.holdingRegisterRead(3015)*(18.4/265);
TT442_SMR_TUBE2_OUT=modbusTCPClient6.holdingRegisterRead(3016)*(18.4/265);
TT443_SMR_TUBE3_OUT=modbusTCPClient6.holdingRegisterRead(3017)*(18.4/265);
TT444_SMR_TUBE4_OUT=modbusTCPClient7.holdingRegisterRead(3012)*(18.4/265);
TT445_SMR_TUBE5_OUT=modbusTCPClient7.holdingRegisterRead(3013)*(18.4/265);
TT446_SMR_TUBE6_OUT=modbusTCPClient7.holdingRegisterRead(3014)*(18.4/265);
TT447_SMR_TUBE7_OUT=modbusTCPClient7.holdingRegisterRead(3015)*(18.4/265);
TT448_SMR_TUBE8_OUT=modbusTCPClient7.holdingRegisterRead(3016)*(18.4/265);
TT449_SMR_TUBE9_OUT=modbusTCPClient7.holdingRegisterRead(3017)*(18.4/265);
Serial.print("TT142_SR_FUEL: ");Serial.println(TT142_SR_FUEL);
Serial.print("TT301_HX406_STEAM_OUT : ");Serial.println(TT301_HX406_STEAM_OUT);
Serial.print("TT303_HX504_STEAM_OUT : ");Serial.println(TT303_HX504_STEAM_OUT);
Serial.print("TT306_EJECTOR_STEAM_IN : ");Serial.println(TT306_EJECTOR_STEAM_IN);
Serial.print("TT313_HX402_STEAM_OUT : ");Serial.println(TT313_HX402_STEAM_OUT);
Serial.print("TT319_HX402_STEAM_SYSTEM : ");Serial.println(TT319_HX402_STEAM_SYSTEM);
Serial.print("TT407_STEAM_REFORMER_OUT_LREF : ");Serial.println(TT407_STEAM_REFORMER_OUT_LREF);
Serial.print("TT408_HTS_IN_LREF : ");Serial.println(TT408_HTS_IN_LREF);
Serial.print("TT410_HTS_OUT_LREF : ");Serial.println(TT410_HTS_OUT_LREF);
Serial.print("TT411_FPZ_OUT_LREF : ");Serial.println(TT411_FPZ_OUT_LREF);
Serial.print("TT430_SMR_TUBES_INLET : ");Serial.println(TT430_SMR_TUBES_INLET);
Serial.print("TT511_SILICON_CARBIDE_OUT : ");Serial.println(TT511_SILICON_CARBIDE_OUT);
Serial.print("TT512_SILICON_CARBIDE_OUT : ");Serial.println(TT512_SILICON_CARBIDE_OUT);
Serial.print("TT513_HX504_IN : ");Serial.println(TT513_HX504_IN);
Serial.print("TT514_HX504_OUT : ");Serial.println(TT514_HX504_OUT);
Serial.print("TT441_SMR_TUBE1_OUT : ");Serial.println(TT441_SMR_TUBE1_OUT);
Serial.print("TT442_SMR_TUBE2_OUT : ");Serial.println(TT442_SMR_TUBE2_OUT);
Serial.print("TT443_SMR_TUBE3_OUT : ");Serial.println(TT443_SMR_TUBE3_OUT);
Serial.print("TT444_SMR_TUBE4_OUT : ");Serial.println(TT444_SMR_TUBE4_OUT);
Serial.print("TT445_SMR_TUBE5_OUT : ");Serial.println(TT445_SMR_TUBE5_OUT);
Serial.print("TT446_SMR_TUBE6_OUT : ");Serial.println(TT446_SMR_TUBE6_OUT);
Serial.print("TT447_SMR_TUBE7_OUT : ");Serial.println(TT447_SMR_TUBE7_OUT);
Serial.print("TT448_SMR_TUBE8_OUT : ");Serial.println(TT448_SMR_TUBE8_OUT);
Serial.print("TT449_SMR_TUBE9_OUT : ");Serial.println(TT449_SMR_TUBE9_OUT);*/
//read acromag 4
switch(TC_CHECK_COUNTER){
case 1:
if(CURRENT_MILLIS - PREVIOUS_MILLIS_3 >= 3000){
TT301_HX406_STEAM_OUT=modbusTCPClient4.holdingRegisterRead(3013)*(.07);
if(TT301_HX406_STEAM_OUT>1000){Serial.println("TT301_HX406_STEAM_OUT > 1000C");FSM_STATE=0;ERROR=13;}
if(TT303_HX504_STEAM_OUT>1000){Serial.println("TT303_HX504_STEAM_OUT > 1000C");FSM_STATE=0;ERROR=14;}
//if(TT306_EJECTOR_STEAM_IN>1000){Serial.println("TT306_EJECTOR_STEAM_IN > 1000C");FSM_STATE=0;ERROR=15;}
if(TT313_HX402_STEAM_OUT>1000){Serial.println("TT313_HX402_STEAM_OUT > 1000C");FSM_STATE=0;ERROR=16;}
if(TT319_HX402_STEAM_SYSTEM>1000){Serial.println("TT319_HX402_STEAM_SYSTEM > 1000C");FSM_STATE=0;ERROR=17;}
PREVIOUS_MILLIS_3=millis();
TC_CHECK_COUNTER=2;
case 2:
//read acromag5
if(TT407_STEAM_REFORMER_OUT_LREF>1000){Serial.println("TT407_STEAM_REFORMER_OUT_LREF > 1000C");FSM_STATE=0;ERROR=18;}
if(TT408_HTS_IN_LREF>1000){Serial.println("TT408_HTS_IN_LREF > 1000C");FSM_STATE=0;ERROR=19;}
//if(TT410_HTS_OUT_LREF>1000){Serial.println("TT410_HTS_OUT_LREF > 1000C");FSM_STATE=0;ERROR=20;}
if(TT411_FPZ_OUT_LREF>1000){Serial.println("TT411_FPZ_OUT_LREF > 1000C");FSM_STATE=0;ERROR=21;} //current issue with reading
//if(TT430_SMR_TUBES_INLET>1000){Serial.println("TT430_SMR_TUBES_INLET > 1000C");FSM_STATE=0;ERROR=22;} current issue with reading
if(TT511_SILICON_CARBIDE_OUT>1000){Serial.println("TT511_SILICON_CARBIDE_OUT > 1000C");FSM_STATE=0;ERROR=23;}
TC_CHECK_COUNTER=3;
case 3:
if(CURRENT_MILLIS - PREVIOUS_MILLIS_3>=3000){
if(TT512_SILICON_CARBIDE_OUT>1000){Serial.println("TT512_SILICON_CARBIDE_OUT > 1000C");FSM_STATE=0;ERROR=24;}
if(TT513_HX504_IN>1000){Serial.println("TT513_HX504_IN > 1000C");FSM_STATE=0;ERROR=25;}
if(TT514_HX504_OUT>1000){Serial.println("TT514_HX504_OUT > 1000C");FSM_STATE=0;ERROR=26;}
if(TT441_SMR_TUBE1_OUT>1000){Serial.println("TT441_SMR_TUBE1_OUT > 1000C");FSM_STATE=0;ERROR=27;}
if(TT442_SMR_TUBE2_OUT>1000){Serial.println("TT442_SMR_TUBE2_OUT > 1000C");FSM_STATE=0;ERROR=28;}
if(TT443_SMR_TUBE3_OUT>1000){Serial.println("TT443_SMR_TUBE3_OUT > 1000C");FSM_STATE=0;ERROR=29;}
TC_CHECK_COUNTER=4;
case 4:
if(TT444_SMR_TUBE4_OUT>700){Serial.println("TT444_SMR_TUBE4_OUT > 1000C");FSM_STATE=0;ERROR=30;}
if(TT445_SMR_TUBE5_OUT>700){Serial.println("TT445_SMR_TUBE5_OUT > 1000C");FSM_STATE=0;ERROR=31;}
if(TT446_SMR_TUBE6_OUT>700){Serial.println("TT446_SMR_TUBE6_OUT > 1000C");FSM_STATE=0;ERROR=32;}
if(TT447_SMR_TUBE7_OUT>700){Serial.println("TT447_SMR_TUBE7_OUT > 1000C");FSM_STATE=0;ERROR=33;}
if(TT448_SMR_TUBE8_OUT>700){Serial.println("TT448_SMR_TUBE8_OUT > 1000C");FSM_STATE=0;ERROR=34;}
if(TT449_SMR_TUBE9_OUT>700){Serial.println("TT449_SMR_TUBE9_OUT > 1000C");FSM_STATE=0;ERROR=35;}
TC_CHECK_COUNTER=1;
TT407_STEAM_REFORMER_OUT_LREF=modbusTCPClient5.holdingRegisterRead(3012)*(18.4/265);//for superheat condition check
TT408_HTS_IN_LREF=modbusTCPClient5.holdingRegisterRead(3013)*(18.4/265);//for superheat condition check
void integrityCheck(){
Serial.println("Checking Signal Integrity.");
PT213_RO_PRESSURE = (modbusTCPClient2.holdingRegisterRead(3021)*(.0125))-50;//ref:43028 read Channel 5 PT213
// if(PT318_HX406_OUTPUT_PRESSURE>=240){FSM_STATE=0;ERROR=3;}
// else{ERROR=0;}
// if(PT213_RO_PRESSURE>=240){FSM_STATE=0;ERROR=4;}
// else{ERROR=0;}
if(PT420_STEAM_EJECTOR_PRESSURE>=240){FSM_STATE=0;ERROR=5;}
else{ERROR=0;}
if(PT304_TWV308_INPUT_PRESSURE>=240){FSM_STATE=0;ERROR=6;}
else{ERROR=0;}
//analog outputs
modbusTCPClient1.holdingRegisterWrite(0x12,OFF);//write channel 0 (BLWRSpeed) to 10 volts
modbusTCPClient1.holdingRegisterWrite(0x13,OFF);//write channel 1 (WP_Speed) to 10 volts
modbusTCPClient1.holdingRegisterWrite(0x14,OFF);//write channel 2 (FCV134) to 10 volts
modbusTCPClient1.holdingRegisterWrite(0x15,OFF);//write channel 3 (FCV205) to 10 volts
modbusTCPClient1.holdingRegisterWrite(0x16,OFF);//write channel 4 (FCV141) to 10 volts
//digital outputs
modbusTCPClient3.coilWrite(7,OFF);//XV801
modbusTCPClient3.coilWrite(13,255);//BLWR_EN ON bc opposite
modbusTCPClient3.coilWrite(14,255);//WP_EN ON bc opposite
modbusTCPClient3.coilWrite(9,OFF);//TWV308
modbusTCPClient3.coilWrite(6,OFF);//XV1100
modbusTCPClient3.coilWrite(5,OFF);//XV501
modbusTCPClient3.coilWrite(8,OFF);//TWV901
modbusTCPClient3.coilWrite(4,OFF);//xv909
if(!(FCV134_BURNER_FUEL_FLOW_FB<0.1)){ERROR=2;FSM_STATE=0;SENSOR_INTEGRITY_CHECK=false;}
else{SENSOR_INTEGRITY_CHECK=true;}
void readOCI(){
Serial.println("Reading OCI417.");
OCI_RESULT=NODE.readInputRegisters(OCI_INPUT_STATUS_REGISTER,2);//address,qty
//do something with data if read is successful
if (OCI_RESULT==NODE.ku8MBSuccess)
OCI_INPUT_STATUS_WORD = NODE.getResponseBuffer(0);
Serial.print("OCI INPUT WORD: ");Serial.println(OCI_INPUT_STATUS_WORD,BIN);
DUN_ZSL = bitRead(OCI_INPUT_STATUS_WORD,1);//PROOF OF CLOSURE
DUN_PSH = bitRead(OCI_INPUT_STATUS_WORD,4);//PRESS SW VALVE PROVING
DUN_PSL = bitRead(OCI_INPUT_STATUS_WORD,5);//LOW GAS PRESSURE SWITCH
COMBUSTION_PRESSURE_SWITCH = bitRead(OCI_INPUT_STATUS_WORD,7);//COMBUSTION AIR SW
OCI_OUTPUT_STATUS_WORD=NODE.getResponseBuffer(1);
Serial.print("OCI OUTPUT WORD: ");Serial.println(OCI_OUTPUT_STATUS_WORD,BIN);
BMM_PROOF_OF_FLAME=bitRead(OCI_OUTPUT_STATUS_WORD,0);
if(FSM_STATE>6 && BMM_PROOF_OF_FLAME==false){FSM_STATE=0;ERROR=10;}
BMM_ALARM_STATUS=bitRead(OCI_OUTPUT_STATUS_WORD,1);
OCI_TO_BMM_COM=bitRead(OCI_OUTPUT_STATUS_WORD,2);
void preTransmission()
digitalWrite(MAX485_RE_NEG, 1);
digitalWrite(MAX485_DE, 1);
void postTransmission()
void readBtn(){
Serial.println("Reading Buttons.");
//read if there has been a change for the inputs
//function for reading buttons and signaling indicators
if(!modbusTCPClient3.connected()){modbusTCPClient3.begin(serverA2,502);}
if(modbusTCPClient3.inputRegisterRead(3002)){
if(bitRead(modbusTCPClient3.holdingRegisterRead(26),15)){
ESTOP_FLAG=true;ERROR=1;
modbusTCPClient3.coilWrite(1,0);
modbusTCPClient3.coilWrite(3,0);
if(ESTOP_FLAG==false){
if(bitRead(modbusTCPClient3.holdingRegisterRead(26),2)){
AMB_BTN_FLAG=true;GRN_BTN_FLAG=false;
modbusTCPClient3.coilWrite(3,1);
if(bitRead(modbusTCPClient3.holdingRegisterRead(26),0)){
GRN_BTN_FLAG=true;AMB_BTN_FLAG=false;
modbusTCPClient3.coilWrite(1,1);
error map
1-estop
2-fcv134 timeout integrity check
3-pt318 over 250psi
4-pt213 over 250psi
5-pt420 over 250psi
6-pt304 over 250psi
7-super heat error
8-No Flame detected
9-Steam gen timeout
10-Loss of Flame
11-Burner reach 800 c timeout
12-Temperature > 1000C
13-temp error
14-
15-
16-
17-
18-
19-
20-
21-
22-
23-
24-
25-
26-
27-
28-
29-
30-
31-
32-
33-
34-
35-
36-