Three phase Voltage measurement using zmpt101b

Here we have 420V between L1 and Neutral and 220-240V between L1 and L2

That makes no sense.

In a symmetrical three-phase four-wire wye system, the three phase conductors have the same voltage to the system neutral. The voltage between line conductors is V LL = sqrt(3) V LN

The sensor can safely measure the voltages between neutral and any of the lines is a standard three phase system.

Please post a link to an official document describing the system you are talking about.