It's not a real accurate device.
At 0.2 LPM the error is +/- 0.266 LPM, which means that if you are actually measuring 0.2 the real flow could be anywhere between -0.066 and 0.466. At 50 LPM the error is +/- 4.25 LPM
i used this but in pipe no flow still showing me values in minus -1.2 mls to 6 mls
// Define the analog input pin (for sensor's voltage output)
const int sensorPin = A0; // Connect the sensor output to A0
// Flow rate parameters for SM7050 (4-20mA to 0.2-50 LPM conversion)
const float minVoltage = 0.88; // Voltage corresponding to 0.2 LPM
const float maxVoltage = 4.4; // Voltage corresponding to 50 LPM
void setup() {
// Initialize Serial Monitor for debugging
Serial.begin(9600);
Serial.println("Starting flow rate measurement...");
}
void loop() {
// Read the analog value from the sensor
int sensorValue = analogRead(sensorPin);
// Convert the sensor value (0-1023) to a voltage (0-5V)
float voltage = sensorValue * (5.0 / 1023.0);
// Compute the flow rate using the given formula
float flowRateLPM = (14.148 * voltage) - 12.25;
// Convert flow rate from LPM (liters per minute) to mL/s (milliliters per second)
float flowRateMLsec = flowRateLPM * 1000.0 / 60.0; // 1 LPM = 1000 mL / 60 seconds
// Print the flow rate in mL/s to the Serial Monitor
Serial.print("Flow Rate: ");
Serial.print(flowRateMLsec);
Serial.println(" mL/s");
// Add a small delay for readability (1 second)
delay(1000); // Update every 1 second
}
It's not a real accurate device.
At 0.2 LPM the error is +/- 0.266 LPM, which means that if you are actually measuring 0.2 the real flow could be anywhere between -0.066 and 0.466. At 50 LPM the error is +/- 4.25 LPM
thats why i am getting - value even there is no flow in real ?
Yes
i used this but in pipe no flow still showing me values in minus -1.2 mls to 6 mls
That makes sense. Any flow below about 0.5 could show a negative value, which means real flows below 0.5 cannot be measured
Maybe this sensor was not the best choice for you application.
Hi, @js13ropa
How are you testing your flow sensor?
Can you draw a diagram or post some pics ofy our test arrangement.
When you have zero flow, you still have a constant head of water connected to the input of the sensor.
How are you measuring the actual flow to calibrate the sensor?
Thanks.. Tom....
If you are trying to measure low flow rates like below 1LPM then that sensor was not a good choice.