Modbus rtu - Serial UART - Understanding some basics

Hi,

I purchased a module to read a pressure sensor. The module says it communicates with serial uart which I thought would make it easy, but then after I got it and started playing with it, realised its not just normal UART serial. Its Modbus RTU uart.
Here are some images from the product on how to send commands:

In the example included above, I'm trying to understand what do all the numbers in the send and recieve lines mean.
For example, send line is: 01 03 00 00 00 02 C4 0B
Just comparing things, I'd say 01 = device ID
03 is just a mandatory number as per the 'Send format' table?
00 00 indicates the start of the register commands/references. And it's not just 00 because the 'Send format' table says it has to be 2 bytes? is that why its 00 00 instead of just 00?
00 = reference to the register table and says read the sensor frequency
02 = reference to the register table and says read the temperature from channel 2?
Question 1: Is the above interpretation correct?

Then C4 0B is a checksum, 2 byte/16 bit crc value that I do not know how to determine, but from reading I understand its some math or bit manipulation of the first 6 bytes of data in that string?

If i'm just doing the same command over and over again, I assume that means the CRC value would be the same? For example if I wanted to just keep requesting the vibrating sensor frequency and temperature on channel 2, then I can just send the above send command (01 03 00 00 00 02 C4 0B) and the crc value will always be the same?

If you cannot tell I am no software engineer. Any help is much appreciated.

Thanks!

There are many descriptions of Modbus RTU on the web, much more comprehensive then any answer here.

Yes. However I would suggest even if you are sending the same known message, it would be better to use one of the many Modbus libraries, e.g ModbusMaster, then you would not have to worry about message formatting, and it will also do things like check for valid responses.