I am using PZEM-004 CT 100A sounds like a creaking sound when connected to a cable with a current below 10A.
I haven't connect it to PZEM. Could you let me know what's the problem is?
I moved your topic to an appropriate forum category @pa3461163
In the future, when creating a topic please take some time to pick the forum category that best suits the subject of your topic. There is an "About the _____ category" topic at the top of each category that explains its purpose.
you should not leave a CT (Current Transformer) secondary without a load - it can generate a very high voltage (see The Current Transformer)
the "creaking sound" you reported in post 1 was probably due to this high voltage being generated when the load was switched on
ALWAYS connect a CT to a burden resistor or measuring device if the load is activated
That's likely the problem.
The CT must be connected to the circuit board, that has the matching burden resistor on it.
The coil itself generates very high (arching/sparking) voltages without that burden resistor.
Leo..